A
airwave1882
Hi I've been given the task of wiring up a 2 phase spot welder, after being told to go and just plug it into a 16 amp socket I found out it takes 43 amp and so told them it needs a hole new circuit. I read the manufactures instructions and found it said for the machine they have. I need 10mm cable on a 45amp 3 phase rcd. Can't get a 45amp 3 phase rcd only 40 or a 63. I can get a 50 amp mcb. So the question is can i put the 63amp 3 phase rcd down line of the 50 amp mcb ? Thanks Lee