A

airwave1882

Hi I've been given the task of wiring up a 2 phase spot welder, after being told to go and just plug it into a 16 amp socket I found out it takes 43 amp and so told them it needs a hole new circuit. I read the manufactures instructions and found it said for the machine they have. I need 10mm cable on a 45amp 3 phase rcd. Can't get a 45amp 3 phase rcd only 40 or a 63. I can get a 50 amp mcb. So the question is can i put the 63amp 3 phase rcd down line of the 50 amp mcb ? Thanks Lee
 
Are you sure the manufacturers specify an RCD? It's highly unusual for this type of equipment. There's no reason I can see that you can't install the RCD upstream or downstream of the OCPD.
 
Have you any details or a link so we can see what the manufacturer has written, agree rcd is unusual in this case and also who told you to plug it into to 16amp outlet? .... are you not the Electrician here, unless you were just following your bosses orders in which case tell him he's a numpty.

To be told the cable size too sounds strange unless its just saying about the flex and plug needed on the unit.

Wire a 63amp 3ph outlet with the appropriate cable for the installation calcs the plug and play would be the normal routine here but I'd be ringing tech' services and asking about the rcd recommendation?
 
Just a quick heads up,recently at our farm we've bought a lot of new equipment,welders,plasma arcs etc and a lot of this gear mentions the use of an RCD,maybe it's a new thing the manufacturers are recommending for transportable equipment.
 
I wouldn't of put one in. It's just that information says put an rcd in. The other spot welder which is a mobile one not bolted down like this one hasn't got an rcd.

I had been told there was a 3p socket for me to wire it into, but on arrival it was only 16 amp. 3phase.
Going to ring manufacturer its a surewekd spot welder. Sureweld PB PBP Pedestal Rocker Arm
 

Reply to 2phase spot welder. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an old Migatronic Automig X 200 welder configured as 380V 3-phase unit. Migatronic for spec. I have a 220V 3-phase point in my garage...
Replies
4
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I have a double oven connection unit. Fed with 4mm cable,40 amp MCB. Hob connected to it with 4mm cable. Bought new oven,stated 16 amp but with...
Replies
3
Views
2K
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock