markthespark

Hello i have been asked to install an oven that is 3.6kw, i am wondering whether this would be fine plugged into a socket behind the existing oven taking into account diversity.

or whether i need to put it on its own radial supply.

Is there anyway of fusing a ring main down to 16amps?

Thanks.
 
Well I can tell you now I have a 3.6kw cooker on a plug top in my house, it has worked flawlessly for years. Please don't listen to my advice though.
 
Hello i have been asked to install an oven that is 3.6kw, i am wondering whether this would be fine plugged into a socket behind the existing oven taking into account diversity.

or whether i need to put it on its own radial supply.

Is there anyway of fusing a ring main down to 16amps?

Thanks.

What do the Manufacturers Instructions tell you??
 
The manufacturers instructions will likely require a 16A connection. I've been called to two of these this month - it seems that that a lot of the new ovens require a larger supply than the old ones.
 
Hello i have been asked to install an oven that is 3.6kw, i am wondering whether this would be fine plugged into a socket behind the existing oven taking into account diversity.

or whether i need to put it on its own radial supply.



Is there anyway of fusing a ring main down to 16amps?

Thanks.

I have noticed most ovens that used to come already fitted with a 13Amp plug,now just have terminals for you to connect your own cable and I think there is a clue there (manufacturers are aware that a 3.6kw oven may work fine on a 13Amp plug ...for a while.) . When you go to cook Christmas dinner and the oven is working at full capacity for long hours then i would consider diversity to be a bit of a red herring mainly used by lazy and/or incompetent fitters, to avoid installing a new 20Amp radial,so they just throw it in a socket designed for 13 Amps max despite the appliance being capable of pulling 14 amps..!
A 3.6kw cooker needs a 4mm hofr (heatproof) cable from cooker to 20Amp isolation point,then feed isolation point in 4mm pvc twin + earth and protect circuit with 20Amp ocpd.

Have you ever seen what a 2kw heater can do to a plug top? Putting a modern oven on a plug is what you call sailing close to the wind
 
I have noticed most ovens that used to come already fitted with a 13Amp plug,now just have terminals for you to connect your own cable and I think there is a clue there (manufacturers are aware that a 3.6kw oven may work fine on a 13Amp plug ...for a while.) . When you go to cook Christmas dinner and the oven is working at full capacity for long hours then i would consider diversity to be a bit of a red herring mainly used by lazy and/or incompetent fitters, to avoid installing a new 20Amp radial,so they just throw it in a socket designed for 13 Amps max despite the appliance being capable of pulling 14 amps..!
A 3.6kw cooker needs a 4mm hofr (heatproof) cable from cooker to 20Amp isolation point,then feed isolation point in 4mm pvc twin + earth and protect circuit with 20Amp ocpd.

Have you ever seen what a 2kw heater can do to a plug top? Putting a modern oven on a plug is what you call sailing close to the wind
No I haven't what happens?
 
It's only a thought but 7671 RECOMENDS that any fixed load over 2KW ought to be on it's own circuit
 
Like this?
698a70ffbcb829e40adb3c775f1b8b87.jpg


---- job chasing that socket in though....
 
is 8 amps big connected to a 13 amp plug top?

If the plug has got a 3 Amp fuse in it,then yes ,8 Amps is big.
I think you are avoiding the not insignificant point that it is not good practice to try to protect equipment with a potential operating current of 14 Amps on a 13 Amp plug. No amount of lateral thinking or outright belligerence will change the fact. 14 Amps with 13 Amp protection = No.
 

Reply to 3.6kw oven on a 13amp plug top. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
867
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
783
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
208
Evening all, I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock