Discuss 3 Legged Ring ??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
0
Hi guys, I have found a 3 legged ring main during an EICR, it’s 2.5mm TnE with a 16A MCB & no RCD Protection. As it measures a S a ring between any 2 of the 3 legs, can a 32A RCBO be Installed or should it remain at 16A ?
 
Hi guys, I have found a 3 legged ring main during an EICR, it’s 2.5mm TnE with a 16A MCB & no RCD Protection. As it measures a S a ring between any 2 of the 3 legs, can a 32A RCBO be Installed or should it remain at 16A ?

That doesn't sound like a correctly wired Ring Final Circuit if you are getting continuity between any 2 out of the 3 legs. Are the readings similar on each pair of legs and do they tally with the expected length of the circuit? R1+R2 also?

There is no such thing as a '3 legged ring', so you'd need to track down where the legs go and fully understand what's going on before increasing the protection. It may be a RFC but with a radial also installed to one point (for some weird reason). Or there may be a cable or wiring fault that is giving you an inaccurate continuity. Were the IR readings OK?

It may well have been placed on a 16A for a good reason, because of previous testing - or because the installer had no idea what he was doing...
 
That doesn't sound like a correctly wired Ring Final Circuit if you are getting continuity between any 2 out of the 3 legs. Are the readings similar on each pair of legs and do they tally with the expected length of the circuit? R1+R2 also?

There is no such thing as a '3 legged ring', so you'd need to track down where the legs go and fully understand what's going on before increasing the protection. It may be a RFC but with a radial also installed to one point (for some weird reason). Or there may be a cable or wiring fault that is giving you an inaccurate continuity. Were the IR readings OK?

It may well have been placed on a 16A for a good reason, because of previous testing - or because the installer had no idea what he was doing...
Dartlec - great response , thanks very much
 

Reply to 3 Legged Ring ??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
465
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock