Hi folks,

I'm installing a 3-ph 32A 60309 socket and just wanted to double check my design calcs are right...

The circuit will be part of a 3-ph sub-board (200A main switch) supplied by our main 3-ph distribution board. The final circuit length is approx 30m. The sub board comprises just power/lighting, no inductive loads, motors etc.

Ib = 32A
In = 3-ph 32A type C (there's already a spare MCB in the board)

Going for an XLPE SWA cable, clipped direct, no other rating factors play a part.

4mm carries 42A, but going for a 6mm because cost isn't a factor and would rather err on the side of too much capacity!

EFLI calcs:
Measured Zs @ DB = 0.05
R1+R2 calculated from table F8A in the IET design guide = 0.2214 ((3.08/1000*30)+(4.3/1000*30))
Total Zs = 0.2714
Max measured Zs for 32A type C = 0.54 ... disconnection times satisfied

Volt drop calcs:
Board supplied by 95mm SWA 109m run, 3-ph.
Pre-diversity total = 463A
Diversity applied as per OSG appendix A = 247A
Diverstiy applied as per IET design guide (0.9 lighting 0.1 power) = 141A

I've based calcs on a figure about 1/2 way between the 2 diversity values = 180A

Volt drop to sub-board = (109m x 180A x 0.45)/1000 = 8.8V

Volt drop on final circuit = (30m x 32A x 6.8)/1000 = 6.5V

Total volt drop = 15.3V ... volt drop less that 5%


Adiabatic calcs:
fault current at end of run:
1.1 x 230V / 0.2714 = 932A
932A = disconnection time of 0.1s for MCB

0.95 x 230V / 0.2714 = 805A

Worst case: S = √( 932 x 932 x 0.1) / 51 = 5.78mm

CSA of 6mm 4-core armouring = 38mm ... adiabatic compliant.



Many thanks in advance to anyone who has the time to help me with this, still learning it all at the moment, lots to consider!

All the best,

Tom.
 
Looks a pretty comprehensive job at first glance. :thumbsup:

Only thing I would correct would be the tabulated current carrying capacity. You have used table 4E4A for XLPE thermosetting cable at 90 degrees, but unless you can guarantee all connections, terminals, and accessories will be rated for 90 degrees as well as the cable you should be using table 4D4A for 70 degree PVC SWA
 
I doubt the volt drop for the lighting circuits from the sub board actually comply. Rule of thumb is to use 2% for submains which allows some leeway for final circuits.
 
Looks a pretty comprehensive job at first glance. :thumbsup:

Only thing I would correct would be the tabulated current carrying capacity. You have used table 4E4A for XLPE thermosetting cable at 90 degrees, but unless you can guarantee all connections, terminals, and accessories will be rated for 90 degrees as well as the cable you should be using table 4D4A for 70 degree PVC SWA

Hi Andy, a big thanks for the reply, and yes a good point I hadn't considered there.. 6mm PVC should still do the job.

T
[automerge]1574171086[/automerge]
I doubt the volt drop for the lighting circuits from the sub board actually comply. Rule of thumb is to use 2% for submains which allows some leeway for final circuits.

Hi West, thanks for the reply, you're probably right - I'll do some calcs for my own morbid curiosity - but thankfully I had nothing to do with that bit of the design!

T
 

Reply to 3 phase design process in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
not to sure on how to find the wats for the power cable calcs could anyone help me its for a ring with 3 Dubble sockets on DB05-3L2 cable size...
Replies
4
Views
1K
I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock