As above really, Massive green house converted into small units.
Basic supply was single phase and when he asked for 3 phase this is what they ve done.
Basicly you ve got 2 phase and netural from one cable and a seperate earth, 2nd cable has 1 phase another CPC.
Its a private supply, All this is connected into a metal clad box.
I only noticed because i was getting a very high Ze reading and traced it back. There are 3 CPC's tagged down to said box.
Where i found a loose connection and got my Ze back down.
Any views commets etc etc This box is Pre meter by the way.