Iainmc123
I have been asked to rigged up a temporary generator for a hotel who have been cut off by the supply autorites for an unpaid bill the generator may have to run for a couple of weeks. Its a 150kva 3 phase generator I connected everything up put an earth rod in the ground and connected to generator frame. when i connect the earth from the generator to the hotels main switch it trips the generators 3 phase rcd switch. I think it could this be a neutral-earth fault within the hotel. when i have the earth from the generator disconnected at the hotels main switch i still get a reasonable EFLI probably through parrell paths as the supply authorities earth and neutral are both disconnected. Is there any danger if i put another seperate earth rod in for the hotels side and leave the generators earth disconnected(the frame still connected to its own earth rod). I dont install generators very often so is there any other reason apart from neutral-earth fault within the hotel that the generator main switch would trip when the earth is connected? any advice would be appreciated
Iain
Iain