A customer has asked me to install a supply for a Wenger Webcot kiln.

The faceplate is very worn and I cannot see the kW. They state the kiln it type 3670w and is rated at 12kW.

The paperwork does have 3670w on it but when I look at the spec sheet (see picture 2, SpecSheet) ) there is no sign of a kiln which is 12kW. This model has 12 elements therefore it must be one of the last 6 models on the spec sheet, but again no sign of 3670w. It looks like there is one called 3060w though but this is not 12kW. Does anyone have any ideas how I could find the kW, or does anyone recognise the kiln details and know the kW?

The wiring diagram (see picture 4) shows that it can be wired as single phase or 3 phase. This will be wired as single phase. My questions...

1. Do I just join the 3 phases together as per the diagram?
2. Do I need to increase cable size compared to the existing flex on the Kiln as I am joining 3 x 10mm cables into one conductor? Although the neutral carries the same current and there is only 1 neutral conductor! Why is this?
3. On the spec sheet (pic 2) it has 2 columns for electricity supply required. One for single phase and one for 3 phase. The last 4 columns for single phase have a dot. looking below it says treat as nominal rating 14kW for single phase, yet the actual column labelled nominal electrical .loading states different, higher values, why is this?

Pictures below show the almost unreadable faceplate, spec sheet, cable and part of the wiring diagram.

Picture 1, faceplate.
3 phase kiln questions? (1)faceplate - EletriciansForums.net

Picture 2, Spec sheet.
3 phase kiln questions? (2)Spec sheet - EletriciansForums.net

Picture 3, Cable
3 phase kiln questions? (3)Cable - EletriciansForums.net

Picture 4
3 phase kiln questions? (4)3P or SP - EletriciansForums.net
 
Try measuring the resistance of the elements.
What csa is the flex currently connected to it.
The existing flex is 5 core 10mm2, although this is a guess. It certainly isn't 6mm and doesn't look big enough to be 16mm.

Measuring the resistance of the elements to what Westward? I'm guessing this will help in determining the kW, but do I use 400v or 230V in the calculation? I will get varying current depending on which is used.

I can just feel myself asking silly questions now. ?
 
I suspect you will need to wire larger 3-core to its internal terminals as if wired single-phase the neutral will be a lot more than 3-phase!

If it is quite old then take care in case it has asbestos thermal insulation inside.
 
Use the ohm scale of a multi-meter we can then probably establish its load for 230 or 415v.
 
If you take the side panel off the kiln there will be the connection terminals for the elements you can measure the resistance of them there to determine the output. The neutral may be for the control side of it. In my sister's kiln the thermostat and timer function are single phase but elements can be wired as either single or 3 phase with links in the connection panel.
It could well be 12-14kw!
Sy
Thinking on it again I replaced the elements on my sister's kiln a couple of years ago and they were 3kw per element and 4 in total.
 
Last edited:
As above you need to measure every element, do not assume they are all the same and ensure they are fully disconnected so you do not get parallel readings (depends on wiring config).

A full pic of the wiring plan would be ideal as oppose to the just the connection points, this will establish how the element wiring is arranged, I am working on a 3ph hot plate atm and it has 6 elements at 7.5 ohms and 2 at 11 ohms, it has 2 sets of 3 elements of 7.5 in series to give 22.5 ohms across 400v ph 1 and 2 and one set of 2 elements of 11 ohms giving 22 ohms ph 3 to balance 8 elements over 3 phase. (of course 3ph goes into 12 easier than into my 8 so would expect your elements are all the same rating)

I suspect without further info you have a 8.5kw or 9.5 kw thus at 230v it is ma 9.5kw and at 400 v 3ph it is 3kw per phase. I guess this by the number of elements and the fact you have the option of 230v or 400v according to the schematic.
 
Last edited:
OK 10mm is promising, but as @westward10 suggest check the resistances (both star and delta if you like, but it will be running as parallel arms of star)

Use the ohm scale of a multi-meter we can then probably establish its load for 230 or 415v.

If you take the side panel off the kiln there will be the connection terminals for the elements you can measure the resistance of them there to determine the output. The neutral may be for the control side of it. In my sister's kiln the thermostat and timer function are single phase but elements can be wired as either single or 3 phase with links in the connection panel.
It could well be 12-14kw!
Sy
Thinking on it again I replaced the elements on my sister's kiln a couple of years ago and they were 3kw per element and 4 in total.
I must apologise for my lack of knowledge here. I have no knowledge of 3 phase as it is not something I ever work with.

What exactly am I measuring between to obtain resistance values?
 
Inside the terminal panel you should see depending on the kiln the ends of the elements terminated sometimes with a bolt through a porcelain insulator or porcelain terminal block. If you disconnect the ends to it at the terminal block you can measure the resistance to work out the kw.
 
Maybe give these people a call?


"We have details, knowledge and specifications for just about every kiln made by Webcot and later, Wenger before Wenger kilns ceased in late 1982. We are truly Wenger Webcot specialists in every manner."
 
With it switched on, do the 6 measurements:
  1. (delta) L1-L2
  2. (delta) L2-L3
  3. (delta) L3-L1
  4. (star) L1-N
  5. (star) L2-N
  6. (star) L3-N
Did you read his last post, he is asking how to measure resistance of the elements and you have instructed him to do a live test for this???? ... unless he wants to blow his meter up this is not a good idea, be clear what you mean especially when live testing please.
 
Did you read his last post, he is asking how to measure resistance of the elements and you have instructed him to do a live test for this???? ... unless he wants to blow his meter up this is not a good idea, be clear what you mean especially when live testing please.
I'm guessing PC just meant to have the on button on, not actually live.
 
Maybe give these people a call?


"We have details, knowledge and specifications for just about every kiln made by Webcot and later, Wenger before Wenger kilns ceased in late 1982. We are truly Wenger Webcot specialists in every manner."
Just emailed them?
 
Did you read his last post, he is asking how to measure resistance of the elements and you have instructed him to do a live test for this???? ... unless he wants to blow his meter up this is not a good idea, be clear what you mean especially when live testing please.
No, I meant the oven controls switched on otherwise he will see infinite resistance at the terminals or cable!

Perhaps I should have been a bit more verbose/explicit about that.
 
One sold on ebay three years ago, and the seller listed technical details, which appear to confirm it is 12kW.
In which case on single phase with the existing cable, and all L conductors connected together, just over 16A down each L. Whereas the N conductor didn't have much, if any, current down it when it was 3 phase, it'll have about 50A on single phase, so you will need to upgrade at least that!
I guess safest to assume 14kW as the total worst case load, so a 60A single phase supply and a cable to match.

Wenger Webcot 3670W Electric Front Load Kiln for Ceramics/Pottery or Glass​

SOLD - 15 Mar 2018, 21:36 £450.00 Buy It Now or Best Offer, eBay Money Back Guarantee

Seller: catspudkin (140) 100%, Location: Totnes, Ships to: Free Local Pickup, Item: 173185872805Wenger Webcot 3670W Electric Front Load Kiln for Ceramics/Pottery or Glass. This kiln is designed for pottery but has been used successfully for glass fusing. The front door can be removed easily to aid transportation/lifting. The kiln was last used 5 years ago and was in good working order. Potential buyers are welcome to arrange to come and look before bidding. External measurements: Height 125cm Width 83cm (including keylock box) Depth 98cm Internal measurements: Height 75cm Width 45cm Depth 50cm 12 kw Three Phase Maximum temp 1300 centigrade Stafford ST301 controller and cabling included
 
Super! I shall measure between the ends of the elements with them disconnected. Would @pc1966 's solution also work (not live of course)?

Could we do an example calculation please?

Lets say the kiln is 12kW. What should the end to end resistance be of each element if wired as single phase?

My maths would give :

230/12000 = 0.0192ohms but is this then multiplied by 12 because of the amount of elements?

I don't think this is correct as if I just changed it for 3 phase I would get 400/12000 which would give a different resistance reading.

What calculation do you do with the resistance reading of 1 x element once you have it?
 
I'm guessing PC just meant to have the on button on, not actually live.
Possible but at best his post is ambiguous and at worst it is dangerous advice given the previous posts.. we mustn't assume you or others would read the post correctly hence I asked for more clarity.

If however he did mean as you express then it will not likely work like that, heating processes of this size will most likely be contactor controlled or even solid state relay via a temp' controller so switchin the kiln on with no power will not link you to the elements and most likely will give you readings of the control equipment, if he meant testing at the elements themselves then it begs the question of why anything needs to be in a on position, until we get a response back I am a tad confused and think the advice is not relating to recent posts but earlier ones.



EDIT @pc1966 you replied while I was typing, ok fair response but you can see why it is a little ambiguous, but as above you will see infinite resistance anyway unless you are testing from the output of the contactors or direct onto the elements, with no power you have no power circuit pulled in for the elements.
 
Last edited:

Reply to 3 phase kiln questions? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock