Hi,

hopefully someone can help or put me straight on this.

i have a 3 phase/415v motor which is 11kw - 15kw, 15A - 28A depending what voltage is applied in either star or delta.

measured the winding resistance which is 0.55ohms between the 3 phases.

now i do think this winding resistance is a good result, but i am a little confused as volts/resistance=amps (1.73 x 415/0.55 = 1305amps!!!

how can this be right?
 
because the impedance of the motor winding are mostly inductive . you can't measure this with an ohm meter or multimeter.
 
Exactly the same is true of a transformer - the DC resistance of a winding will be much lower than V/I. The resistance does not tell you anything about the characteristics of the device as a whole, only about the wire with which it is wound.

The lower the DC resistance the better because winding resistance wastes energy, but there is a practical minimum resistance that can be achieved with copper wire for a given size of motor or transformer. The aim is always to make it a very small fraction of the inductive reactance, so that most of the supply voltage is used to do work and very little is wasted producing heat.

Taking your motor as an example, if it has a resistance of 0.55Ω between lines, each coil is 3/2*0.55=0.825Ω. At 15A line current, the current per coil will be 15/sqrt(3)=8.7A. The total resistive heat loss will be 3 x 8.7 x 8.7 x .825 or 185W of heat wasted in overcoming the resistance of the copper.
 

Reply to 3 phase motor current calculation - from winding resistance in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
636
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock