I am wiring 3 3 phase motors, 1.1 KW each via 3 STOP/START manual starters. If one starter locks out for any reason, the others also need to close down simultaneously.

I initially thought that I would have to have a relay in each starter connected in series but I've realised that won't achieve what I want.

The other alternative is to bring the supply into a contactor, then to the TP/N distribution board out to the starters but this would mean I believe that each starter from the auxiliary contact would have to be connected back to the contactor coil so that whichever motor locked out would open the contactor.

Is this correct?

Thanks in advance
 
If you mean that you want all to stop if overload of any trip then if control voltage is all common you just run you stop circuit in series through each overload first before going to your individual start stop buttons for each contactor.
 
Last edited:
View attachment 11905
Three individual starters.
As usual didn't read the OP fully.
I read the O/P's query different, i believe he wants to have individual start stop for all 3 motors but if one faults and trips he want the other two to drop out too, so your overloads in this diagram should be in series up front of control and 2 additional start buttons also you missed off.
 
Ah! missed that but still think he wants any overload to drop out all contactors, and also having one start might mean he has one stop and thus makes sense to series overloads, if the O/P can confirm this for us?
 
Last edited:
If you look how it works, all three contactors have to be closed for it to maintain. I've only been using this system for 40 years on conveyor systems.
A little colour may make it clear
View attachment 11906
 
Last edited by a moderator:
If you look how it works, all three contactors have to be closed for it to maintain. I've only been using this system for 40 years on conveyor systems.
Soz tony think im tired i zoomed in and saw you contactor ref'are alternate, i know you dont need to be taught to suck eggs ive been on here long enough but tonight i think that it for me.... must be overworked lol..
 

Reply to 3 Phase Motors & Control Gear in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

When working in a control panel. If I needed to replace a 3 phase contactor do I need to carry out a 10point check to prove dead on just the mains...
Replies
16
Views
1K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
313
Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
785
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
392

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock