I have recently started on a site where there is a 16A 3 phase Atex socket which is supplied by a 16A 3 phase MCB. It was picked up on a recent inspection that it needs an RCD. For the life of me I cannot find a 16A 3 phase RCD. I started to think does it really need an RCD? The socket is only used for one piece of equipment which is regularly maintained and only used by trained operators. The building in which the socket is in is not used very often as it is a warehouse and power is off to the socket when the building isn’t occupied.
Any advice greatly appreciated
 
I cannot find a 16A 3 phase RCD

Are you looking for an RCD or RCBO? If RCBO then Tel has found you an example above. If you just want an RCD to use downstream of the existing 16A MCB then a 25A or 40A device will be much more readily available and probably cheaper.
 
Would it be possible to remove the socket and replace it with an isolator, thus removing the requirement for RCD protection?
A risk assessment would have to show a good reason why an RCD is not required in this case, documented and attached to the existing certification.
The Napit Codebreakers book has a whole 18 page chapter on the subject of risk assessments for the omission of RCDs:
16257634890722202848007688318230.jpg
 
I have recently started on a site where there is a 16A 3 phase Atex socket which is supplied by a 16A 3 phase MCB. It was picked up on a recent inspection that it needs an RCD. For the life of me I cannot find a 16A 3 phase RCD. I started to think does it really need an RCD? The socket is only used for one piece of equipment which is regularly maintained and only used by trained operators. The building in which the socket is in is not used very often as it is a warehouse and power is off to the socket when the building isn’t occupied.
Any advice greatly appreciated
Used 25, 40 and 63 amp 3 phase RCDs and then fitted fused switched isolators after the RCD so can downgrade to suit. This was in oil and gas industry too setting up life testing in workshops and also on sites.
 
Would it be possible to remove the socket and replace it with an isolator, thus removing the requirement for RCD protection?
A risk assessment would have to show a good reason why an RCD is not required in this case, documented and attached to the existing certification.
The Napit Codebreakers book has a whole 18 page chapter on the subject of risk assessments for the omission of RCDs:
View attachment 87507
Needs to be a socket as the equipment does get moved about. Thanks for the info much appreciated
 
Here’s a thing about those particular RCBOs….. the 4p neutral is just a dummy. So what that means is that inside a 3ph board you end up ‘losing’ 2 adjacent phases if you’re only populating with 3ph devices. AND - as I found to my distress on a recent job, they only do that on the right hand side - on the LEFT bus you end up with the N as L1 which means when you come to present cable you end with Blk-Gry-Brown, miss two, and it just looks so wrong!! ?
 

Reply to 3 Phase RCD? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
674
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
514
Hi guys, I am rewiring a commercial launderette with 3 phase machinery. Does the machinery need to be RCD protected being in commando sockets...
Replies
5
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock