Hi All
I’m in a bit of a quandary at work and need a couple of things clearing up if poss. I’m the maintenance manager/spark/fitter/skivvy/everything else that needs doing man
in a plastics factory and I’ve got to provide a supply for a new machine.
The current set up is a 90mm SWA protected by a 250a MCCB in the main distribution panel and is 30m in length to the first machine, then is paralleled into another isolator supplying a second machine (if that makes sense?).
We are replacing the first machine and I’m just not sure if it’s acceptable to piggy back from one machine to another? My instinct is that it’s not, but for the life of me, I can’t find anywhere in the regs to say that it’s not.
The machines have a combined power of 130kW, which works out at 335A and 90mm armoured is good for 251A using installation method E as it’s in traywork. This leads me to my second concern in that the cable isn’t rated high enough. It was installed before I started with the company and it has been running like that without issue, so before I go to my boss and tell him I need to spend £££’s on more cable etc, can somebody provide me a smoking gun, or better still, tell me it’s ok.
I haven’t had chance to measure the Zs readings, but I should be able to do that tomorrow during downtime.
Thanks I’m advance
Thanks I’m advance