Discuss 3 phase to single phase conversion in the UK Electrical Forum area at ElectriciansForums.net
arkin
Been asked to do a conversion of 3 phase 4 wire supply to a single phase . Swap 3ph mcb for appropriate single , identify two of the cores as brown and blue at both ends make the other two earth. Re calc volt drop for 230 . Any objections?
The load will have been balanced over the phases it is to be assumed and the original 4core sized to suit... you now are loading it all onto 1phase and this may compromise the ccc of the cable.
You need to calculate the load and do a calculation as if you were supplying a new cable and see if you require a bigger supply or not.. you could always have 2ph/2N with the 4 cores use the swa as earth and add additional earthing as you have effectively doubled the core size but not increased the csa of the armour. Run an earth equal to or larger than the new Phase size (2x XXmm cores) and if you are extending the equipotential zone through this submains then this will have to be added to the earth size.
I was always taught to make any spare cores into cpc. And besides that running separate earth is out of the question, far to difficult and quite long run. I originally though like billb, just take a phase and n from isolator. But the vd has to be treated differently as really this is now a 230v circuit. Maybe I'm reading too much into it.
The roller shutter could be industrial sized but still tend to be small motors ... im surprised the roller shutter wasn't spec'd for the existing 3ph supply seems a cock up on their part either way you ned the motor rating to know if the existing is ok, as we lack info here about the existing we can't advice much.
Not really looking for advice on sizing cables or protective devices, that's not a problem. Just wasn't sure if I was going too far, and maybe should just take a ph and n at isolator.
Reply to 3 phase to single phase conversion in the UK Electrical Forum area at ElectriciansForums.net
Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
I have a single phase stainless steel pasteuriser that has two control boxes attached to it. One box houses the control for the electronics and...
Hi, As a DIYer I`ve quite a bit of wiring up domestic house single phase experience but no 3 phase experience. So I have been offered a two post...