What's the norm on a 3 phase Submain in regards to swa and earthing, I'm looking at 25mm swa but not keen on using the armour as earth, (it works out ok size wise) I normally use an extra core for earth on single phase but 5 core swa seems a bit thin on the ground anyone have fors and againsts for usin the armour?
 
Yeah it's quite a long run underground, I know how to gland etc its not that so much it's if it's damaged underground and a bit of water gets in the armour and rots away, I'm just belts and braces I suppose lol what's the best way to terminate the earth if using the armour I normally go for serated washers and bolts I don't think they make pirahna nuts that big!
 
That's the plan handy, but you never know if a stone gets in etc and gets a slight slit in the sheath just go carefull I suppose, softly softly catchy monkey
 
The use of the SWA is one of the big differences in common practice between domestic and commercial/industrial installs. Using the armour is common practice as earthing conductor although recent installs I have been involved with supplementary has been specified within switch rooms. This provides extra protection on ladder and cable tray.
 
If you're worried about damage to the cable on installation or backfilling of the trench, why not put a duct in first and just pull it through?

How are you going to damage a cable with back fill if done properly?
Do the job properly, use the armour, gland and earth the end correctly. Can’t be any simpler really.

If you’re worried you can carry out a sheath test. But if it fails you’re shafted anyway.
 
What's the norm on a 3 phase Submain in regards to swa and earthing, I'm looking at 25mm swa but not keen on using the armour as earth, (it works out ok size wise) I normally use an extra core for earth on single phase but 5 core swa seems a bit thin on the ground anyone have fors and againsts for usin the armour?
look, if the armourings are adequate then whats the need for the spare core?...
and i say spare core as that`s exactly what it would be.....doing nowt....lol...
 
How are you going to damage a cable with back fill if done properly?
Do the job properly, use the armour, gland and earth the end correctly. Can’t be any simpler really.

If you’re worried you can carry out a sheath test. But if it fails you’re shafted anyway.

I better off not go back and some tests on my garden jobs!
 
What's the norm on a 3 phase Submain in regards to swa and earthing, I'm looking at 25mm swa but not keen on using the armour as earth, (it works out ok size wise) I normally use an extra core for earth on single phase but 5 core swa seems a bit thin on the ground anyone have fors and againsts for usin the armour?

Single phase SWA...........3 core dedicated earth.
3phase/N. SWA.........5 core with dedicated earth( neutral distributed or not).
That's me every time.....bwtfdik:)
Solid 6mm brass bolt and nut earth throughout.

Nothing wrong with either method mate...........properly installed lol

- - - Updated - - -
 

Reply to 3 phase in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
686
If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
Replies
7
Views
1K
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
929
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
275
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock