Has the heating requirements been calculated properly?

you may find that 3 x 1kW heaters would be enough.....



or..... you need something like 3 x 2.5kW!
 
not exactly calculated, but as I’m installing a 4mm ring circuit, I’ll probs upgrade to 2kw heaters
Why a 4mm RFC? it is a recommendation that loads of > 2KW have their own dedicated circuit, IMO a 4mm RFC is the wrong solution.
 
But that recommendation is mainly aimed at people who may put large loads on a ring which is used for other things as well. This ring is purely for the 3 hears.
you maybe correct, still don't like it
 

Reply to 3 x 1.5kw heaters on one circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
246
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
756
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
839
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock