Discuss 3 zone S plan plus with UFH problem in the Central Heating Systems area at ElectriciansForums.net
V
v.elec
Hello.
I have wired an S plan plus system. 1 zone for DHW, 1 zone for CH and 1 zone for UFH (underfloor heating).
3 channel programmer, 3 motorised valves, cylinder stat, room stat for UFH, no stat for CH & 2 pumps.
Honeywell motorised valves, Horstmann 3 channel programmer, Grundfos pumps and Potterton system boiler
Here is the problem guys.
Switch the central heating on and everything is fine. HW and UFH - it all works. HOWEVER, HW and UFH only work if heating is ON. A.k.a, they are not independently controlled.
Three orange switched live from valves all going into same terminal together to switch on boiler and pump.
Room Stat signals MV via brown wire which turns on underfloor heating
Cylinder stat signals MV via brown wire which turns on hot water.
Programmer has direct switched live to MV brown wire, a.k.a, no room stat.
I think it may be the wiring centre, but I can't think of what mix up of wiring would cause Zone 2 and Zone 3 to only work when Zone 1 is.
Hope you can help. Thanks.
Hello.
Sounds like these not a permanent power supply to the grey wire on both the HW and UFH zone valves to me I would check that first.
Ok Elrick, I will check that next week. Thanks.
Would that be the reason because the orange wire from the ONLY heating valve is turning on the boiler? Therefore, the HW + UFH can operate without it's grey wire? Just I'm sure I connected them into perm live terminal on 12 way block. I will defo check next week.
Yes as the brown on the zone valve opens the valve allowing the water pass though the valve and the grey is a permanent supply to a micro switch that makes when the valve opens sending power to the boiler via the orange
Get a heating engineer in who knows about 'S' plan zoning, wiring and diagnostics.
Where are you? If your local to me I'll help you out for a modest fee.
Hundreds of miles away.
I am an electrician. I have wired a few S plan and Y plan before. This was already wired however, but incorrectly and unsafe with no enclosures or containment, so I disconnected it all and had to trace and ring out wiring. It was like the guy before only used what he had, bits of single wire going into boiler and connector block taped up...etc. One of the wires which is grey is not actually grey, it was blue but sleeved grey with 2no 3 core HOFR flex in parallel.
It is easier to wire from scratch, compared to fixing someone else mess and making it work.
I agree that it's easier to rewire from scratch but a custard doesn't want to pay for non-essential rewiring work when a simple diagnostic job is all that's needed.
Ps
I've wired many hundreds of Y, S, Multizone and three wire 'Guaranteed Warmth' systems over the years, particularly when I was installing the heating systems too.
They are all pretty simple once you understand the circuit diagram.
Ps
Yeah, they are. But I ain't paying you to fix it. Went early this morning, it's fixed now. Thanks Elrick.
Reply to 3 zone S plan plus with UFH problem in the Central Heating Systems area at ElectriciansForums.net
Hi all, I've noticed that my UFH pump is not always turning on as soon as the stat & valve calls for heat. This results in hot water passing...
Hi does anyone have a S plan wiring diagram that incorporates a third zone to accommodate an underfloor heating system like polypipe? Would...
i , i have a property to work on which has a programmable room stat upstairs and a programmable roomstat downstairs. S plan system , 2 zones. hot...
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
A combi is heating 5 ufh zones downstairs and 1 radiator zone upstairs. It has a two port valve for each. My question is, would you fit this with...