I have been asked to do a landlord safety check on a 1st floor flat the board is a 4way wylex rewireable unit and im just wondering if i can still pass this as there will be no additions just the safety check?
 
Advertisement - Content continues below
J

Jurassic Spark

  • Thread Starter Thread Starter
  • #2
Just class it as 2 (needs improvement) on the periodic form and suggest they be replaced with Wylex plug-in MCBs
 
T

Tapouchoke

  • Thread Starter Thread Starter
  • #3
3036 rewirable fuses in 1st floor flat

With reference to the above I had the niceic man out yesterday for my yearly visit now he told me a code 2 was a unsatisfactory under 17th regs
Assuming the flat is old and cables buried in walls
also there is no rcd protection for cables concealed in wall or partions
Which you would give a code 4 to
But remember your name is on the periodic

hope this helps
 
J

jibspark

  • Thread Starter Thread Starter
  • #4
3036 rewirable fuses in 1st floor flat

With reference to the above I had the niceic man out yesterday for my yearly visit now he told me a code 2 was a unsatisfactory under 17th regs
Assuming the flat is old and cables buried in walls
also there is no rcd protection for cables concealed in wall or partions
Which you would give a code 4 to
But remember your name is on the periodic

hope this helps
wow so does that mean that no install pre 17th will be a full pass on a periodic?
 
A

adamh

  • Thread Starter Thread Starter
  • #6
i dont think i got the job anyway lol
 
J

Jurassic Spark

  • Thread Starter Thread Starter
  • #7
NICEIC are up there own arses - the Regs aren't retrospective. The current Regs only apply to work carried out NOW. Any work carried out in the past was applicable to the Regs at that time.
If I bought myself a car from the 50s, I wouldn't be expected to fit seat belts in it!
 
B

bigal

  • Thread Starter Thread Starter
  • #8
Don't forget the rating on the 3036 in a domestic is only 1ka (at least it was before 17th). So you'll have to compare that to the PFC incoming.
bigal
 
J

jaldred

  • Thread Starter Thread Starter
  • #9
Remember, code 4 only means "does not comply with current regulations".
Code 4 would apply to every installation that does not have rcd protection on cables buried in walls except blah blah.....
Code 4's do not equate to an unsatisfactory periodic report.
 
I

iceman

  • Thread Starter Thread Starter
  • #10
hi i just been to test an installation witch has BS3036 rewirable fuses cos the person was sayin the lamps keep blowin upstairs did insulation resistence test tht was fine 299M ohms did a loop test and tht came in at 279ohm my verdict was possable overload also did insulation resistence oh heating sully cable found a fault between line and neutrel reading wos 1.08 not rite att all wot do recken fellas???

supply thts ment to be lol cheers
 
Last edited by a moderator:
S

Spudnik

  • Thread Starter Thread Starter
  • #11
Did the isolator for the CH have a neon?

Did you isolate the CH system before the test?
 
I

iceman

  • Thread Starter Thread Starter
  • #12
yes everythin was isolated cheers
 
I

iceman

  • Thread Starter Thread Starter
  • #14
no it was deff 279 ;-) no rcd protection
 
:eek::eek::eek::eek: then your ir readings a the least of your worries try and get them to have a 17th ed cu fitted
check to see what earthing system the flat has if its not tt something has gone wrong, even on tt i would be aiming for 100ohms at cu
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to 3036 rewirable fuses in 1st floor flat in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members
Advertisement - Content continues below
Top Bottom