Discuss 3036 rewirable rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
57
have a customer with a 3036 rewireable board. i Need to provide rcd protection for 1x30a ring circuit and 1x5a lighting circuit for additions. my plan is to remove the ring main and lighting circuit from existing fuse board.

From one of the now spare ways run a 6mm2 t+e fused at 40a to a new 2way 63a 30ma C.U. the ring main now on 32a mcb and lighting 6a mcb both circuits now rcd protected.

anyone see any issues ??
 
is not replacing the D.B. a better option? for a few quid more than you are already spending on the additional 2way board complete you could get a full 17th edition board, im sure a chat with your customer is what you need to do, spend now save later and flexibility to expand.
 
just done a quick cable calc re correction factor for a 3036 fuse.

6mm2 rated current 45Amps 45x0.725 = 32.625 (In Max)
10mm2 rated current 65Amps 65x0,725 = 47.125 (In Max)

it = in/Cc 40/0.725 = 55.17

ib=38<In=40<Iz=65

so my original plan to use 6mm no good will have to be 10mm feed to 2nd cu.
 
Last edited:
apart from a new dual rcd main C.U any other options for providing rcd protection to both circuits.

just thought only one lighting circuit/ ringmain my oriiginal plan would put both on single rcd which i want to avoid. Im hoping they will opt for a complete new main cu.
 
Last edited:
just out of interest, is it the older 1mm cpc in the RFC? if so i think your option of new door separate db is best. as 2.5/1mm will not meet disconnection time for 30a 3036
 
1mm more than likely cannot take the fault current to operate the OCPD in the required time.
If it is 1.5 there is the option of fitting a rcd after the consumer unit, in a 2w enclosure for each cct.
Although i personally think your options are the way to go :)
 
Connect the new circuits into a small enclosure containing 2 RCBO's for lights / sockets.
Feed this unit with 6mm T&E using one of the spare fuseways fitted with a wylex
plug-in 40A mcb , saves having to derate due to rewirable :)
 

Reply to 3036 rewirable rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
612
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
627
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock