Discuss 30mA RCD protection required for existing circuit? in the UK Electrical Forum area at ElectriciansForums.net
spud1
If I was replacing an existing light fitting in a domestic premises, making no alteration or addition to the circuitry, would I then be obligated to provide that circuit with 30mA RCD protection if it didn't already have it?
If it’s a “like for like” swap, then there’s no need to install an RCD, but you could just mention it to the customer and explain it would increase the safety of the circuit inline with the current regs.
I think the purpose of the regulation is that this is a job that is highly likely done by the householder or DIY'er and therefore gives increased protection. I think that it applies to new and rewired domestic lighting circuits for when the householder goes to change a standard pendant fitting to a decorative one. For RCD protection to be required on an existing installation when the householder wants to change a fitting would be costly and in most cases impractical. And in this case, the risk is reduced as it is done correctly by someone engaged that is competent.
Would you issue a Minor works cert for a like for like light fitting replacement!?
Yes as I would carry out basic inspection and testing to ensure the circuit is safe and fit for continued use.
Fair enough, when replacing accessories or light fittings like for like, I usually make a note of a Zs and or any RCD test readings etc. where applicable on the job sheet for my reference, I don't normally go as far as issuing a MWC to the client but maybe I should start...?
Completely up to you. Either method suits as all the client will do is shove it a drawer and forget about it.
How would you do that if you are mot changing it to a dual RCD split one?
Unless if you fit an RCCBO on that cct.
What would you do with the other ccts in the board wjich are not RCD protected?
Sorry for the rant but you don't have to.
Reply to 30mA RCD protection required for existing circuit? in the UK Electrical Forum area at ElectriciansForums.net
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Hi all Was looking in to the adibatic equasion as our company will not let us add on to a Ring circuit with 1mm cpc.. I want to give some...
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...