Have a 3a FSU that feeds an adjacent WC light and fan, wired from a socket that is a spur. Even though we all know that it's safe (no different to having a 3a plug top in the socket), can't quite make up my mind if it's compliant or not. Thoughts?
 
spur from a spur. not compliant.

hate to disagree, but whether its a socket, or a 3A fcu... still a spur from a spur.
Perfectly safe, as you say, it could be a double socket with a 3A plugged in... no difference to the load on the cable branching off the ring.... but regs is regs
 
OK - the two polar opposite responses I expected. This application is fixed equipment…
 
My reading of 433.1.204 suggests to me that it’s compliant

“…..Such circuits are deemed to meet the requirements of regulation 433.1.1 if the current carrying capacity (Iz) of the cable is not less than 20A and if, under the INTENDED conditions of use, the load current in any part of the circuit is unlikely to exceed for long periods the current carrying capacity of the cable.”
 
spur from a spur. not compliant.

hate to disagree, but whether its a socket, or a 3A fcu... still a spur from a spur.
Perfectly safe, as you say, it could be a double socket with a 3A plugged in... no difference to the load on the cable branching off the ring.... but regs is regs
There is in fact no reg that says a spur off a spur is not allowed.
We don’t do it because the example diagrams of ways to comply with the only RFC reg don’t show it but it’s perfectly possible to comply with spurs off spurs.
I’ve done it in a large hotel lobby with 5A sockets for table lamps.
 
This is an interesting question.

It goes against the design guide in appendix 15 (no spurs off spurs allowed). However, I don't believe there is any reg stating that app 15 has to be rigidly adhered to in order to comply.

IMO if the total load won't exceed the current carrying capacity of the cable running back to the ring, then it is compliant. In this case 20A for the double socket, and 3A for the FCU = 23A. So compliant if Method C.

Best practice? Perhaps not, the fused spur could easily be repurposed for a higher load. And you can bet a fiver of anyone's money that the next spark would condemn it, as it doesn't meet app 15.
 
Could we also go down the “fixed load” route as a light and a fan aren’t going to overload anyway? Tongue in cheek - no overload protection required unless manufacturer requires it for fan!
 

Reply to 3a FSU downstream of a spur socket from RFC - compliant? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
655
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
637
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Hi! I've got a couple of 32A Wago clips. Creating a spur socket from a ring circuit with these is quite easy, but I wanted to know if it's...
Replies
10
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
257

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock