Discuss 3P+N socket testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
You would use a phase rotation tester.
Consult a industrial electrician.
A phase rotation tester can be used to test polarity but isn't necessary....unless you want to test phase rotation.
Polarity testing involves individually checking each phase and neutral to earth, each phase to neutral and between each of the phases, to assess correct connection.
Many 'live' testing instruments include phase rotation indicator arrows, these days.
When installing 3 phase supplies, all the polarity testing can be done before the system is made live, via continuity test.
Reply to 3P+N socket testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...