Hi, i have a 3 ph tyre changer here which seems to have lost power. Everything works ok when doing small size tyres but the motor wont turn when trying to removing a larger size tyre, it just hums. The motor seems fine when checked with a multimeter. However the switch has one phase live at all times. The other swap as they should do when the switch is operated between forward and reverse. Should the wire that isn't swapped to obtain reverse, be live even when the switch is in neutral? What else could cause a lack of power?
Thanks for any advice help
TH
 
Hi, i have a 3 ph tyre changer here which seems to have lost power. Everything works ok when doing small size tyres but the motor wont turn when trying to removing a larger size tyre, it just hums. The motor seems fine when checked with a multimeter. However the switch has one phase live at all times. The other swap as they should do when the switch is operated between forward and reverse. Should the wire that isn't swapped to obtain reverse, be live even when the switch is in neutral? What else could cause a lack of power?
Thanks for any advice help
TH
Best advice Tom get a Sparks to do some testing
 
Hmmmmm.
A 3-phase motor won't generally start at all with a phase missing, so it seems likely that the supply is all there, although deserves checking for correct voltages on-load. My next check would be to current-clamp all 3 lines and compare with nameplate FLA. This will give a better indication of possible motor problems than a continuity test with a multimeter. Lines equal and overloaded would suggest a mechanical problem e.g. geartrain binding at higher torque. Lines unequal would suggest a motor winding fault. Etc.
 
this is likely to be a fairly simple job for any spark used to dealing with 3 phase motors.
where in the country are you?
 
Hmmmmm.
A 3-phase motor won't generally start at all with a phase missing, so it seems likely that the supply is all there, although deserves checking for correct voltages on-load. My next check would be to current-clamp all 3 lines and compare with nameplate FLA. This will give a better indication of possible motor problems than a continuity test with a multimeter. Lines equal and overloaded would suggest a mechanical problem e.g. geartrain binding at higher torque. Lines unequal would suggest a motor winding fault. Etc.
I've just finished checking the supply and all voltages are there and within a few volts of each other. The windings are showing as correct I.E continuity where it should be no continuity between phases. I suspect now that you might be right when you say mechanical fault. I'll probably take the bevel box out and check the bearings etc.
My main concern now,electrical wise , is should one line be live at all times, even with the switch in the middle/neutral position? This one line stays live while the other two are not live in neutral and swap over depending which direction you use.
 
Are you a car mechanic in a French garage? The neutral you're talking about seems to be referring to being mechanically out of gear.
 
should one line be live at all times, even with the switch in the middle/neutral position

This is an economy method used to control 3-phase motors with a 2-pole reversing switch. The windings remain live in the stop position so the switch does not serve as an isolator. In the good old days, smaller 3-phase machine motors without starters would sometimes be controlled with a DP toggle switch; we last had this on a gang drill from the 1940s that we retired in the late 90s.

If the control is instead a 3-pole switch and all three lines visit it, then it's more likely that one pole is welded shut.
 
This is an economy method used to control 3-phase motors with a 2-pole reversing switch. The windings remain live in the stop position so the switch does not serve as an isolator. In the good old days, smaller 3-phase machine motors without starters would sometimes be controlled with a DP toggle switch; we last had this on a gang drill from the 1940s that we retired in the late 90s.

If the control is instead a 3-pole switch and all three lines visit it, then it's more likely that one pole is welded shut.
The neutral I refer to is 'off' I.E Forward, off/neutral, reverse.
It is a 3-pole switch, which is why i thought it odd that one remained live. I'll pull it out tomorrow and see if i can check that it is indeed welded shut. If it is I might just swap to single phase and do away with the only equipment I have that is 3 phase. I have a suitable motor and switch just waiting for something to come along that I can use them in.
I can then use the motor on my lathe (in another building without 3 phase) using an inverter for speed control instead of having to swap belts around.
Thanks for all the help i'll let you know if it is welded contacts.
 

Reply to 3Ph switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
480
I have a pressure washer that I got as part of "a good deal", actually an exceedingly good deal as I later found out. I've had it a while, I guess...
Replies
5
Views
1K
Hello guys. I have a question as being in Africa for 15 years, I used to use a mustimeter to check voltages at the light switches as they got...
Replies
5
Views
772
Hello I have an old timed extractor fan in the bathroom which has stopped working. It has 3 wires which are black, brown and grey. I believe that...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock