1

1valiant

Am I missing something here or is it just plain bad luck? I've recently tested a fuseboard and the RCD failed (MEM A100HE 100AMP 30Ma RCD). Sent off for a new one and it failed got another failed again.
Checked multi-tester on another board, tester works fine. It's on a TN-S system, there's a 16mm earth clamped onto the incoming leading straight to the fusebord, the earth clamp is tight. all bonding is good. Am i missing something or have I just come across a batch of dodgy RCCB's.

Cheers.
Darren.
 
What tests are you doing on them? Remember an insulation test will blow them.

PS you say RCCB at one poiint and RCD at another - which do you mean?

Edit. Sorry I normally associate RCCB with incommers, but technically this is not so.
 
Last edited:
To be sure we're understanding this, it's failing all 3 (possibly 5) of those tests???

So it trips at 0.5X ? (coz that's the only way it would fail ... it shouldn't trip at all).
and
It doesn't trip, in time, at 1X 30ma (0 or 180 degrees)
and
doesn't trip, in time, at 5X 30ma (0 or 180 degrees) ?

In the latter 2 (4) cases is it not tripping at all or taking longer than 411.3.2.2 dictates (0.4S for your TNC-S 230V system).

I'd be double checking my wiring in the CU first. Ensure you have reconnected the main earth after testing Ze and ensure that you have no temporary links anywhere.

What is the Ze you have and where are you performing the tests for this (32A RFC at the socket for example?)?
 
I am going to take a guess that you are not testing at source, and applied loads are screwing up the testing
Either that or you are extra unlucky :)


If I'm wrong I am sorry :D
 
This might be of interest.

LINK

If the RCCB operates when you press the test button but not when applying a 30mA test using your meter then you may be experiencing the same problem i had yesterday.
 
Just Googled the RCCB in question, guessing it's from a Memera 2000 CU which is the same CU i had the issues with the RCBO on. The RCD in that board tripped very slowly (180ms on x1) which seemed odd but still a pass. This was with my croc clips clamped to the neutral bar and the busbar at the base of the RCCB. Thinking even more now that you might be having the exact same problem so try plugging your meter in at a remote socket on the ringmain and give it a whirl. Obviously ensure all equipment has been disconnected from the socket circuit you are testing from as some electronic gear will not appreciate losing power 4 times in quick succession.
 
Yes, it sounds like the same problem it's a Memera 2000CU. and I'm testing from a radial coming out next to the board. No equipment on circuit, Ze 0.05. very frustrating,

Darren
 
I have a similar problem an rccb A100HE with trip times of 98ms and 40ms, obviously not suitable for current regs and I put it down to age. Have been looking for a replacement and found the following literature:
http://www.neweysonline.co.uk/neweys/pdf/Eaton_Memora_Protective_Devices_&_Accessories_Technical.pdf
Within this booklet from Eaton it lists the A100HE as being 30ma and 40ms but on further reading found this paragraph
30mA​
providing a high degree of protection against electric shockdue to direct contact. The device must be able to trip within 40milliseconds when a fault current of 150mA is detected.
The result is that I believe mine is in its design criteria but that the characteristics of the design criteria and my problem is that the design criteria are not fit for current usage and it is simply not reflected in the simple terminology of the 30ma 40ms that we use today. According to the Eaton website a new unit is available as EAM1002H which is the new designation - interchangeable no idea and will be trying eaton uk later.
 
Ignore my stupidity, at 1x limit is 200ms and at 5x 40ms as per current on site guide and 415.1.1 in the BGB gives 40ms for 5x but NO time against 1x. But I have never seen one this high, installed a wylex last week and had times of 40ms and 19ms and my house this morning is 37ms and 23ms.
Think the watchword is be aware that current kit is very sensitive whereas older kit wasn't but may still be compliant even if we are not used to seeing the numbers!!! So easy to get led by normal and requirements.
 
Welcome to the board sbelec.

Your first post had me worried there. I was just double-checking the numbers in the regs to do a detailed reply when you posted your correction. We all get brain failure from time to time!
 

Reply to 3rd RCCB Fault?? in the Australia area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
790
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
765
1pm, quite happy doing my planned job. Builder then asks if I could go out to another job where the top lights have all tripped out. I like peace...
Replies
9
Views
2K
Hi. Now I'm pretty sure why this is happening, but I thought I'd check. Just did a standard RCD test at a client, and the RCD failed the test...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock