Discuss 40 amp max pole? in the UK Electrical Forum area at ElectriciansForums.net
I am looking to add a 240v 50 amp circuit breaker to this panel for a welder. But (in the top left of the pic) is says that it is 40 amp max pole. Am correct to think this means i can only add a 40amp 240 volt circuit breaker?
That 40 means you have 40 spaces to use does it have a spare space for a double pole 40 amp breaker. The panel is a 200 amp panel
[automerge]1567553677[/automerge]
I misread you can put a 50 amp breaker with #8 wire which is good for 55 amps
I have plenty of spots left. I think 13 total. My only concern is that it is a stab lok panel.
If 8 AWG NM cable, a 40A breaker is max, Home Depot & Lowes do carry the UBI UL classified breakers for FPE, be aware those ChiCom breakers are not cheap. Because of the issues with FPE Stablok panels and being obsolete I recommend replacement.
Reply to 40 amp max pole? in the UK Electrical Forum area at ElectriciansForums.net
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...