40 amp max pole? 20190903_170109 - EletriciansForums.net

I am looking to add a 240v 50 amp circuit breaker to this panel for a welder. But (in the top left of the pic) is says that it is 40 amp max pole. Am correct to think this means i can only add a 40amp 240 volt circuit breaker?
 
View attachment 51880

I am looking to add a 240v 50 amp circuit breaker to this panel for a welder. But (in the top left of the pic) is says that it is 40 amp max pole. Am correct to think this means i can only add a 40amp 240 volt circuit breaker?
That 40 means you have 40 spaces to use does it have a spare space for a double pole 40 amp breaker. The panel is a 200 amp panel
[automerge]1567553677[/automerge]
That 40 means you have 40 spaces to use does it have a spare space for a double pole 40 amp breaker. The panel is a 200 amp panel
I misread you can put a 50 amp breaker with #8 wire which is good for 55 amps
 
That 40 means you have 40 spaces to use does it have a spare space for a double pole 40 amp breaker. The panel is a 200 amp panel
[automerge]1567553677[/automerge]

I misread you can put a 50 amp breaker with #8 wire which is good for 55 amps
That 40 means you have 40 spaces to use does it have a spare space for a double pole 40 amp breaker. The panel is a 200 amp panel
[automerge]1567553677[/automerge]

I misread you can put a 50 amp breaker with #8 wire which is good for 55 amps

I have plenty of spots left. I think 13 total. My only concern is that it is a stab lok panel.
40 amp max pole? 15675569807167248801639345031096 - EletriciansForums.net
 
If 8 AWG NM cable, a 40A breaker is max, Home Depot & Lowes do carry the UBI UL classified breakers for FPE, be aware those ChiCom breakers are not cheap. Because of the issues with FPE Stablok panels and being obsolete I recommend replacement.
 

Reply to 40 amp max pole? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock