Hi guys if you could help me out with this would be much appreciated,

its for a shop within a shopping centre and the client ( Decathlon! ) require a huge
supply which i have contested but they seem to think they need this size feed.

From a ryefield board to a 400amp switch fuse within the switch room using tri rated singles
in metal trunking approximentlt 5 metres away.

Sizing of tri rated singles ?

then from the switchfuse to a 400amp MEM isolator which is 30 metres away , containment
will be ladder rack.

sizing of the 4 core armoured ?

Cheers not my strong point so help would be great.

If there is anything which you need left off il do my best to respond with it.
 
somewhere between 120mm and 150mm at a guesstimate. just look up the ccc's and VD's in the osg and do the calcs. from there.
 
Last edited:
Do Decathlon know they have a contractor with little experience?
what are your cable calc's?

Nothing wrong with abit of advise this is what the forum is about,

They have paid UKPN 3grand to fit 400amp fuses and provide a bigger ct chamber
for the new 250kva supply, the shop is not very big and will have lights and say 10 a/c units
so i have asked why this size of supply is nessesary but ive been told thats what they
require etc etc

a cable which can potentially handle 360amps would be a 185mm but im asking advice to
see if i can use smaller..

Could you be of help?
 
Nothing wrong with abit of advise this is what the forum is about,

They have paid UKPN 3grand to fit 400amp fuses and provide a bigger ct chamber
for the new 250kva supply, the shop is not very big and will have lights and say 10 a/c units
so i have asked why this size of supply is nessesary but ive been told thats what they
require etc etc

a cable which can potentially handle 360amps would be a 185mm but im asking advice to
see if i can use smaller..

Could you be of help?
install ladder racking/tray and you can get away with 150mm singles or it will be a 240mm for 3phase 400amp in free air/tray


table 4d3a and 4d4a for calcs


i bet it will be cheaper to get 3X 150mm and earth than 1 x 240 multicore
 
install ladder racking/tray and you can get away with 150mm singles or it will be a 240mm for 3phase 400amp in free air/tray


table 4d3a and 4d4a for calcs


i bet it will be cheaper to get 3X 150mm and earth than 1 x 240 multicore

Then you have the added implication of non ferrous gland plates and the laying arrangements of them on the ladder.
 
The upstream fusing and cable size may be to meet full disrimination with the fusing within their distribution system and not the calculated load, arguing this point may make you look like a rookie if this has been designed, these are commercial premises and a fault say on a large A/C unit does not want to take all the power out because of poor design and ruin trade.

On here we appreciate it if you show us your calcs, that way we know you are trying to help yourself and not after others to do all the work for you, I'm getting the impression this is beyond your field of experience and on that note you should think hard about trying to do this work without experience, a small error can be very costly.
 
ref method E ( perforated tray/ladder?etc.) gives you 330A with 150mm SWA . it's up to you to decide. too small and you'll have to rip it out. too large and you've caused your client unnecessary expense.
 
So for the 30m run on ladder rack from the 400 amp switchfuse the 400amp isolator which has to be mutlicore aomoured i was calculating 185mm .

i believe i will have trouble terminating this into those outlets.. Might need to use those special crimp packs which turn and reduce to get the cores in.
 
yes, but is the design load 400A or considerably less? it might just be that a 250A supply is insufficient and they've gone for the next standard size up.
 
true but the op said its only going to be 5m or so, not a problem to put in trefoil cleats etc for that distance and with that size cable im sure the op would do a proper job

30M mate :)
 
The upstream fusing and cable size may be to meet full disrimination with the fusing within their distribution system and not the calculated load, arguing this point may make you look like a rookie if this has been designed, these are commercial premises and a fault say on a large A/C unit does not want to take all the power out because of poor design and ruin trade.

On here we appreciate it if you show us your calcs, that way we know you are trying to help yourself and not after others to do all the work for you, I'm getting the impression this is beyond your field of experience and on that note you should think hard about trying to do this work without experience, a small error can be very costly.

I understand where your coming from but im sure im more than capable in installing this work to a good standard im just asking maybe the more experienced in cable calculation to help me keep this size as small as possible as the size of cable is hard to handle and terminate as im sure youve done before.
 
[h=3]Multicore 90°C Armoured Thermosetting Insulated Cables[/h]Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,
Voltage:400V
Load:221.7kW / 400A
Length:30m
Method of Installation:In free air or on a perforated cable tray
Cable Size:150mm²
 
So for the 30m run on ladder rack from the 400 amp switchfuse the 400amp isolator which has to be mutlicore aomoured i was calculating 185mm .

i believe i will have trouble terminating this into those outlets.. Might need to use those special crimp packs which turn and reduce to get the cores in.

There's always the option of using 2 smaller csa multicore cables in parallel. If you do your calcs for this method. It can sometimes work out less and be easier to terminate etc.
 
yes, but is the design load 400A or considerably less? it might just be that a 250A supply is insufficient and they've gone for the next standard size up.

Ofcourse this is why i queried it originally but as i have had no real answers back other than just price for the above 250kva supply which is worst case senario not the loading which may be considerably less.
 
There's always the option of using 2 smaller csa multicore cables in parallel. If you do your calcs for this method. It can sometimes work out less and be easier to terminate etc.

Ive looked at this metod and ive calculated 2x 50mm 4 core swa to achieve the 360amps ruffly does that sound right mate?
 
[h=3]Multicore 90°C Armoured Thermosetting Insulated Cables[/h]Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,
Voltage:400V
Load:199.53kW / 360A
Length:30m
Method of Installation:In free air or on a perforated cable tray
Cable Size:150mm²
 
i estimate 2 x 50mm will give you 326A method E. ( table 4D4A).

have you looked up xlpe? that will give you more as it's rated to 90deg.C, but the problem is that the switchgear you're connected to is probably only 70deg.C.
 

Reply to 400amp 3 phase 4 wire cable sizing help. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
535
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
645
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
898
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock