Unless the Manufacturer’s Instructions say otherwise.
Stationary equipment commercial or domestic does not require RCD protection.
However BS7671 now requires all socket-outlets rated 32A and below to be provided with RCD protection unless in non-domestic installations, a documented Risk Assessment concluding RCD protection is provided.

411.3.3 Additional requirements for socket-outlets and for the supply of mobile equipment for use outdoors
In AC systems, additional protection by means of an RCD with a rated residual operating current not exceeding 30 mA shall be provided for:
(i) socket-outlets with a rated current not exceeding 32A, and
(ii) mobile equipment with a rated current not exceeding 32A for use outdoors.
An exception to (i) is permitted where, other than for an installation in a dwelling, a documented risk assessment determines that RCD protection is not necessary.

The requirements of Regulation 411.3.3 do not apply to FELV systems according to Regulation 411.7 or reduced low voltage systems according to Regulation 411.8.
NOTE 1: See also Regulations 314.1(iv) and 531.3.2 concerning the avoidance of unwanted tripping.
NOTE 2: See Appendix 2, item 11 in respect of risk assessment.
NOTE 3: A lighting distribution unit complying with BS 5733, luminaire track system, installation coupler, LSC or DCL is not regarded as a socket-outlet for the purposes of this regulation.”
 
Unless the Manufacturer’s Instructions say otherwise.
Stationary equipment commercial or domestic does not require RCD protection.
However BS7671 now requires all socket-outlets rated 32A and below to be provided with RCD protection unless in non-domestic installations, a documented Risk Assessment concluding RCD protection is provided.

411.3.3 Additional requirements for socket-outlets and for the supply of mobile equipment for use outdoors
In AC systems, additional protection by means of an RCD with a rated residual operating current not exceeding 30 mA shall be provided for:
(i) socket-outlets with a rated current not exceeding 32A, and
(ii) mobile equipment with a rated current not exceeding 32A for use outdoors.
An exception to (i) is permitted where, other than for an installation in a dwelling, a documented risk assessment determines that RCD protection is not necessary.

The requirements of Regulation 411.3.3 do not apply to FELV systems according to Regulation 411.7 or reduced low voltage systems according to Regulation 411.8.
NOTE 1: See also Regulations 314.1(iv) and 531.3.2 concerning the avoidance of unwanted tripping.
NOTE 2: See Appendix 2, item 11 in respect of risk assessment.
NOTE 3: A lighting distribution unit complying with BS 5733, luminaire track system, installation coupler, LSC or DCL is not regarded as a socket-outlet for the purposes of this regulation.”

Thanks for confirming what I previously said..
Very much appreciated
 
Or he can come on here and ask for advice on other ways to do the job, saving himself lots of unnecessary work and ultimately saving his client money..
Or you can carry on being obtuse and childish..
you have totally ruined this thread for the op and shown to me that you are very childish and petty
 
As far as I can see, you’ve offered no constructive advice at all.
All you’ve done is disagree with people who have.
My advice has been to use a socket with built in RCD, rather than installing a hard to obtain RCD at the CU.
Another option would be to use 63A sockets.

As it stands I doubt anyone could legitimately produce a Risk Assessment which concludes RCD protection is not required.
 
As far as I can see, you’ve offered no constructive advice at all.
All you’ve done is disagree with people who have.
My advice has been to use a socket with built in RCD, rather than installing a hard to obtain RCD at the CU.
Another option would be to use 63A sockets.

As it stands I doubt anyone could legitimately produce a Risk Assessment which concludes RCD protection is not required.

I suggest you read back through the thread from the start!
I have only given constructive advice!
Please prove otherwise..
I have been involved in the installation and repair of commercial catering equipment for 25 years, I am an approved engineer for many brands.
What has been suggested is totally unnecessary..
just because you can’t do something doesn’t mean that it can’t be done, a risk assessment in this instance would be easy enough..
It’s stationary equipment that doesn’t need RCD protection
 
Im not looking for a way round it, just trying to emphasize that as agreed the stationary equipment doesn’t need RCD protection, it’s totally unnecessary..
Or he can come on here and ask for advice on other ways to do the job, saving himself lots of unnecessary work and ultimately saving his client money..
Or you can carry on being obtuse and childish..
you have totally ruined this thread for the op and shown to me that you are very childish and petty

RCD protection isn't required for stationary equipment, this does not mean that it is totally unnecessary as you put it. RCD protection could still be installed for stationary equipment over and above the minimum standards set out in bs7671.

However the OP is installing socket outlets, we don't know why they are installing socket outlets, just that they are.
You've made the assumption that the cooking equipment is to be stationary equipment which could reasonably be permanently connected and that the OP is not working to a specification.
 
reasonable assumptions based on the information he has given and the huge amount of experience I have in this area..
I have designed and installed many commercial kitchens, the information I have given is very helpful.
 
thank you all for your advise.

Installer who is connected the equipment has specified socket outlets.

The catering equipment, i belive will be on wheels for cleaning etc.

From all the info i have recieved there seems to be several ways todo this.

I think i will be taking the route of having an inline rcd for each peice of equipment, i would have prefered go put it in the board but it seems the costs for a hager addon rcd is quite expensive £300 a peice.
The rcd socket also seems like a viable option however i wonder if being directly behind equipent would make it less accessible or in the way due to the size, if its further up the line at least more of the cable is protected.
 
reasonable assumptions based on the information he has given and the huge amount of experience I have in this area..
I have designed and installed many commercial kitchens, the information I have given is very helpful.

I don't think they are reasonable assumptions. No matter how many kitchens you have designed, unless you have seen the design for this kitchen or the specification the OP is working to you can't assume what is required.
Some specifications require socket outlets to be fitted to allow quick replacement of faulty equipment to reduce downtime, removal for deep cleaning or changing the equipment as required.

The majority of my experience of commercial kitchens is for events, so everything is on plugs and sockets. Sometimes this is in fields on generators and sometimes indoors with various three phase outlets provided.
 
I can feel the love in this thread.

I'm currently in negotiations with several major telecoms providers who want socket outlets to power their racks but don't want RCD protection but refuse to do a risk assessment. They are the designers but don't want the responsibility for the risk assessment, rock and a hard place this change to 411.3.3.

I need a beer.
 
Trouble with the courses is they only skim through the regs..
Some of us keep up to date and also know how to apply them accordingly
The last course I did for the 16th edition, was mostly about how to label up the book and doing past papers.
There was some discussion about particular Regs.
In the main the course was designed to help us pass the exam, not learn the Regs.

One of the reasons I’m a member of this and other forums is to keep my knowledge of the Regs up to date.
I know for a fact that I have mentioned this change in the requirements to provide RCD protection for sockets, as have a number of other members.

As for applying the changed requirements, the solutions are to provide RCD protection, produce or have produced a documented RA which indicates RCD protection is not required, or use a socket rated higher than 32A.
 
The last course I did for the 16th edition, was mostly about how to label up the book and doing past papers.
There was some discussion about particular Regs.
In the main the course was designed to help us pass the exam, not learn the Regs.

One of the reasons I’m a member of this and other forums is to keep my knowledge of the Regs up to date.
I know for a fact that I have mentioned this change in the requirements to provide RCD protection for sockets, as have a number of other members.

As for applying the changed requirements, the solutions are to provide RCD protection, produce or have produced a documented RA which indicates RCD protection is not required, or use a socket rated higher than 32A.

We got there in the end
 

Reply to 415v 3 phase sockets and rcd protection. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
686
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
721
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
726
What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Replies
9
Views
828
Hi guys, I am rewiring a commercial launderette with 3 phase machinery. Does the machinery need to be RCD protected being in commando sockets...
Replies
5
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock