Discuss 4mm radial circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
storyelectrical
I've just been flicking through the regs to do some cable calcs for a job and noticed that a 4mm 2 core cable installed using method B (under floors etc) has a capacity of 30A. However it is ok to connect to a 32A MCB for a radial socket circuit. Don't know if its just me missing something (which I'm guessing it probably is!) but that doesn't sound right. I'm looking at table 4D2A. I just can't figure it out!
If the cable is flat twin and earth how come you are using reference method B
installed under floors and buried in non-insulating wall ( e.g. plaster ) then ref. method C. then a 32A MCB is fine.
Hi there. I have exactly the same concern. I have 32A, 4mm radial circuit. The worst case reference method throughout the run is method B in conduit - more exactly I ran the cable in 20mm oval conduit chased into the brickwork - rather than capping (presumably capping not enclosing the cable is not termed as conduit). The tables showing 30A CCC (nearest table that the OSG is based on is multicore in BS7671, which makes me doubt how accurate the 30A figure is) I would expect that this fixing method is quite common. I'm not an experienced electrician so am interested what folk do in this case.
there is no reference method B for T/E. you can't downrate to 100,101,etc. as it's not in thermal insulation. i generally use ref. method C if some of the run is in trunking etc.
"there is no reference method B for T/E" ... yes I saw that. The OSG mentions this and claims the figures for 'multicore cable' are similar. OSG Page 52, Table 7.2 then gives method B for T&E @ 30A. Interesting to hear your experience though - so you run 4mm in conduit on a 32A CB? Cheers
you can run 4mm cable at 32A till the cows come home. it won't get anywhere near 70deg.C.
i would as long as the oval tube is big enough to leave a decent airspace. not if i have to use lube to get the buggers in. LOL.
That's interesting. I thought the airgap in conduit is what performs an insulating function. So I put the 4mm cables in 16mm oval conduit - not really tight, but not really loose,. Thanks for the reply...
What you planning on connecting to the cable? not a block of flats I hope haha, JK, How many sockets out of interest only?
Biff. I think I agree with you BUT strictly speaking the O/C device is rated at 32A, yet the cable is only QUOTED as handling 30A. So I guess the debate is how accurate the Ref Method B for Multicore is VERSUS T&E, in conduit IN the wall. So am I right in assuming you feel this cable method has a CCC of 32A. Cheers...
I'm was actually working out for installing a cooker circuit when I noticed this in the regs. Its just something that I noticed and it triggered me thinking. The regs state that cables run under floors should be classed as method B. But then also show drawings of 4mm radial socket circuits. If I was installing a 32A cooker then 4mm wouldn't be acceptable but for a socket circuit connecting into the same MCB is fine?
read posts #7 , 9 & 11.
and cables under floors are nothing like as derated as conduit values.
why is it not fine ?
Yeah, why didn't I think of that, read replies that had not yet been written :dizzy2:
You should be a politician, answering one question with one of your own. LOL
Reply to 4mm radial circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Came into work today with a fairly urgent requirement to install an instant hot water handwash unit in a small commercial kitchenette/servery -...
Guys needvadvice please I was asked to carry out an annual inspction of a DB recently There are 12 in number radial circuits suppling sockets...
I'm in the process of renovating a house. As I go through room by room I am removing old plaster and as the cables are exposed at this point I...
Hi Doncaster EV ultra cable: Does anyone know what the current capacity of these cables is given particular reference methods? The spec sheet...