Discuss 5.3 kw double oven on a 20 amp fuse with 2.5 cable in the Australia area at ElectriciansForums.net
E
egginyourface
evening all,
I was told to run 2.5 cable from fuseboard to supply a 3.5 kw single oven. Job is done....
Now they've said theyre going to put in a 5.3kw double oven in.
Question i have is can I apply diversity to this and keep 2.5t+e or do i need to run a new 6mm,
advice would really appreciated
thanks
23 amps. Well technically 20amp fuse still exists so the cable is protected subject to normal de-rating considerations. Pushing it a bit IMHO. I think I`d recommend an upgrade in writing so if/when you have to go back to upgrade your covered. Sometimes these ovens have 5.3kw or something on them and that includes 3 elements say 2x grill and 1x rear circular fan element. As its unlikely or impossible perhaps to have the rear fan oven element on at same time as the grill you would be under 20 amps again
as a1guvner says. alteration in design, extra work, extra cost.
the diversity allowance for cooking appliances in a household is 10amps + 30% f.l ( full load if i remember right ) +5amps if the cooker outlet has an incorperated socket outlet.
which gives around 15A without a socket outlet ( top of head as calculator not to hand). so 2.5mm on 20A is adequate. problem would arise if they added a hob or changed to oven for a higher rated one.
just worked it out. 5300/230 = 23A
10A + (0.3 x 13 ) = 13.9A. where did 16.9 come from?
1.divide the watts by 230 to give a total load current figure.
2. apply diversity: 10A + 30% of remainder = answer. add 5A if a socket outlet is incorporated.
are you saying its 30% of whats left of the 23 amps after taking the 10 off? I thought the fl (in the osg) meant full load so 30% of 23 amps (not 13amps) ie 6.9 amps plus the 10
equalling 16.9
So in your case it would be 230/5300= 23a
First 10a than 30% of remainder (23-10=13) 13/100=0.13x30=3.9a. Than add your original 10a on gives you 13.9a, and if you have a socket add 5a so your total would be 17.9a. 2.5 would still be ok but you run future risks if anything changes or they deciede to open their doors to the homeless :p
(PS this calculation does not take into account any factors for the cable run)
and if adding up multiple loads on a single circuit.....so lets say that you have several cookers all fed from one circuit...then you would apply diversity to EACH LOAD SEPERATELY...then add up the total......
this of course will dictate the size of overcurrent device you will use at origin....which in turn will give you the correct cable size to use.....installation method, ambient tempreture, grouping and length of run taken into account of course.....
sorry i meant 30% of the 13 amps
The cable run is about 12metres long and run in yt2 trunking with a 10mm earth for the gas. Only about 1 metre of it is actually buried
Reply to 5.3 kw double oven on a 20 amp fuse with 2.5 cable in the Australia area at ElectriciansForums.net
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
4K
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
  • Locked
5K