Hi there , is there anything else to consider when using 5 core SWA instead of 4 core + separate Earth in three phase installations for cable calcs etc? Apologies but just moving in to the 21st century never used 5 core before
Not if you are using the 5th core as the CPC as it is not a live conductor.
Though you might want to question the need for it when the armour is almost always suitable for use as a CPC.
I must admit, I have found it great when putting in 16A 3phase sockets.
many of them come with threaded entry and not easy to use a banjo or an earth nut to get the cpc to the socket from the armour.
still use a swa gland on the socket end but don’t need to mess with connecting anything to it.
Reply to 5 core swa cable calcs in the UK Electrical Forum area at ElectriciansForums.net
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
I was the 2nd sparks taking over a garden office supply job. The first sparks had fitted 10 sq mm 3 core SWA, but it actually had brown, blue and...
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...