Discuss >50v on megger when doing ELI test in the UK Electrical Forum area at ElectriciansForums.net
Sb8389
Hi guys
I have had an issue with a couple of sockets in a property when carrying out ELI tests on them saying greater than 50v and won't let me test, some sockets are ok on the same circuit just a couple saying this anybody come across this and understand what it means,I'm using a megger and the system is TNCS
Have you checked the sockets internal connections sounds like loss of earth continuity.
sounds weird to me. when performing EFLI test, you should have > 50V, should be 240V. unless it's saying >50V N-E, which could indicate an earth fault.
On my old Megger seperate it means phase neutral reversed or no earth connection .Also excessive voltage between N+E.
I suppose megger have kept the same convention
the megger mft's have 3 voltage indicators. L-N, L-E and N-E. the first 2 light in normal circumstances, the 3rd only if there is a finite voltage seen N-E and the tester refuses to test.
Just retested the sockets and all testing ok only since I found a neutral to earth fault on the leg back to mains and disconnected it not sure how this would affect the issue I have had
Have you totally isolated the faulty part or just disconnected from the board because if it is the latter the fault would still be there on a ring final.
I will vouch though the megger can be a temperamental beast. We purchased 30 of them and had no end of problems. They replaced them all in the end and we ended up buying 30 of the flukes as well because all the sparks were moaning about the megger.
Don't see how a N/E fault would cause this problem.
unless there's a poor N or E connection on the supply side or at origin. i recently had a simar fault which was caused by a loose terminal in the head, on the link connecting the N block to the E block.
Reply to >50v on megger when doing ELI test in the UK Electrical Forum area at ElectriciansForums.net
I've just been to a job to replace a burned out switch where the customer supplied his own Arlec dimmer switch. During a dull moment, I read the...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...