As my Part P assessment draws closer I find myself worrying about possibly silly things, and what I might get asked about on the day!

Today I realised that I've put 5A round pin sockets, for table lamps connected to a dimmer switch next to the door, on a 6A MCB. Now this sounds wrong but I don't suppose that anyone would question putting 5A sockets on a 5A 3036, which is probably worse due to it's higher fusing factor.

I think it's ok, and I don't think that you can get a 5A MCB anyway, but I have this niggling feeling that I might look silly if questioned about it and it turns out to be wrong.

Really just looking for someone to put my mind at rest on this (or tell me if I'm wrong)
 
bear in mind that that 6A MCB is to protect the cable, not the 5A sockets.
 
I could also be looked at as 1 lighting point and therefore be assumed to realistically carry a max 100W lighting load or about 0.5A load well within 5A.
 
Think your set up is fine. In fact you should be happy that you've had the forsight to use round pin sockets. Good shout. ;)

Sent from my GT-I9100 using Tapatalk
 
Thanks guys, that's put my mind at rest. I can get back to worrying about more interesting things now like H&S and documentation :wink_smile:
 
The 5A rating is the maximum they are designed to take.
Just like 20A socket-outlets on a 30/32A CPD.

I would be happy having a 16A load through an old style 5A BS outlet without any fear of overheating or burning , Especially when you see what the Yanks use to carry 16A...lol!! Those old 5A sockets and plugs have at least 3X the brass content, of the Yank, Aussie, and a few other overseas 16A outlet designs... lol!! :shocked3: :lipsrsealed2: :cyclist:
 

Reply to 5A 3-Pin Sockets in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Just looking at starting some testing since newly qualified, don't know if this is a stupid question or not. Is there an allowed...
Replies
5
Views
662
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
1K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
675
Last week I was working in a house changing a socket. When I turned the main switch back on and the MCB on the socket didn't energise. I went and...
Replies
6
Views
852
We have table lamps connected to UK 5A wall sockets (with round pins). Looking for a solution to also charge phone/tablet from this socket (2A...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock