Doing some testing today and came across something I was hoping to get cleared up.

The maz zs of a c type 16amp 61009 is 1.44 ohms on table 41.3 however on table 41.5 it states that a 30ma 61009 under 32amp can have max zs of 1667ohms.

Would you write on test sheet maz zs 1667 ohms and that as long as result is under the 1667 then its ok? Because the recorded result I got was 1.76 ohms which fails first table but is ok in the second one. Confusing lol

Thanks in advance.
 
Doing some testing today and came across something I was hoping to get cleared up.

The maz zs of a c type 16amp 61009 is 1.44 ohms on table 41.3 however on table 41.5 it states that a 30ma 61009 under 32amp can have max zs of 1667ohms.

Would you write on test sheet maz zs 1667 ohms and that as long as result is under the 1667 then its ok? Because the recorded result I got was 1.76 ohms which fails first table but is ok in the second one. Confusing lol

Thanks in advance.

Its your choice, either comply. But if you designed to meet the 1.44 then id be looking as to why its exceeded the value.

Cheers

Cheers
 
What does "doing some testing" comprise ? periodic testing or initial verification ?

Using a RCD as fault protection in a TN-S would be my personal last course of action.
 
What does "doing some testing" comprise ? periodic testing or initial verification ?

Using a RCD as fault protection in a TN-S would be my personal last course of action.

Exactly. On a TN system the 30mA part of the RCBO is for additional protection.
 
It seems from other threads on the same subject, that if conducting an EICR where you are testing an existing electrical installation you can, if the circuit does not comply with the current ADS limitations use the RCD's 1667 ohms as compliance (possibly with a remark being made in the appropriate section of the report). If however you are testing a new installation, then ADS requirements must be complied with whether or not an additional protection device (RCD) is provided.

Personally, i don't particularly agree with that stance as i know, maybe more than some here, just how unreliable RCD devices can be over a period of time....
 

Reply to 61009 rcbo max zs 1667ohms? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
Doing calcs on swa supply to building as sub main from main three phase squard D board for single phase supply off of TN-S supply. I used cable...
Replies
9
Views
1K
Hi, This is my first post, although I have been browsing the forums for a little while now. I work in BMS and have my AM2 on friday. The nature...
Replies
1
Views
2K
S
Has anyone any views on max Zs for say a type c 32a rcbo at 80% is 0.54 and 100% 0.68. I am currently testing a collage and all ring circuits are...
Replies
14
Views
14K
I have a circuit of only approximately 8-9 metres from a 61009 type B 32A Rcbo to an oven & hob all run in m T&E and have got a Zs result on "No...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock