Good morning,
We have a load of approximately 18.5kw ( compressor skid). There is a plan to install a dedicated socket for this machine, the cable route is yet to be finalised and One of the contractors says 16mm2 cable 100A fuse is adequate but this comes from a rule of thumb as opposed to calculation. Is this a common rule for 63A sockets ?

Thanks
 
There isnt really a "common rule" it is entirely dependant upon cable length, installation method/route, size & type of protective device, ambient temps etc etc.

Get it designed properly then come back :)
 
without knowing the length of the run, i'd say 16mm cable on a 63A breaker is closer to the mark. i assume it's 3 phase. that equates to around 30A per phase.
 
You have to base the supply on the socket outlet because it could be used for any purpose.
 

Reply to 63A three phase socket in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Replies
12
Views
724
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hi, We have a three phase 400v socket rated at 63A. It is proposed to use this for a mobile skid. There is an 18.5kw motor and an approximate...
Replies
2
Views
2K
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
1K
Not a 'commercial' job as such but given that three phase is involved I feel it belongs in this section. In my semi-professional cabinet making...
Replies
10
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock