Fairly low it's a 3 bed house, but no heating or hot water there is a small sauna tho.what's the load corrent?
Found it a bit had to calculate as it's 3 phase,The on site guide has tables for this, factors for the conduit for certain lengths and size and factors for the cable. Have a quick look, sounds okay though.
Don't think that's relevent Drew, 4x6mm conductors will have a total factor that needs to be less than the conduit factor. I'll have a look when I get to my van.Found it a bit had to calculate as it's 3 phase,
Not grate but very hard to get 32mm conduit in place.. thank mateThe rating for 6mm is 58 for each conductor, and the conduit rating for 3.5m straight is 290
Don't forget though that this is a guide.
25mm?Not grate but very hard to get 32mm conduit in place.. thank mate
Don't have it in Sweden25mm?
That sounds quite limiting! 32mm is a huge step up from 20mm.Don't have it in Sweden
The rating for 6mm is 58 for each conductor, and the conduit rating for 3.5m straight is 290
Don't forget though that this is a guide.
Where did 32mm come from?Not grate but very hard to get 32mm conduit in place.. thank mate