Correct. Guidance from the NICEIC to it's members now is undersized main bonding cannot be left if alterations and additions are taking place.
To the OP. I had a similar problem recently, I got a plumber to install a short plastic section just beyond the stopcock. Was a lot cheaper and less disruptive than getting a 10mm to it on that job. Might be an option for yours as well and covers your ---.

That's not the case going by the guidance endorsed by the IET, and they write the regs. I'll stick with that.
6mm is deemed adequate in any situation.
 
My house is a very similar build and layout to the OPs. Luckily I had extensive kitchen works done a couple of years ago so I managed to pull in a 10mm bond but it still took me a couple of hours of lifting carpets and cutting chipboard flooring to get the cable in. Annoyingly a few months later I would not have needed a bond as the incomer is plastic and there's no earth potential... :rolleyes:

For a simple board swap this scenario would add a lot to the price of a job and most customers would refuse to have the work done purely for the disruption and mess.

Potentially one method would be to convert the earthing arrangement to TT but then this has it's own inherent issues.

What's to stop some unscrupulous individuals from splicing 10mm onto the 6mm just out of sight to appear to comply with 544????
Im shocked at such a suggestion........;)
 
That's not the case going by the guidance endorsed by the IET, and they write the regs. I'll stick with that.
6mm is deemed adequate in any situation.
So lets say in a non dwelling setting the minimum (based on the supply N) required copper main bonding conductor according to BS 7671 for a TNCS supply is 35mm you'd happily leave a 6mm in place as you've stated it is adequate in any situation?
 
So lets say in a non dwelling setting the minimum (based on the supply N) required copper main bonding conductor according to BS 7671 for a TNCS supply is 35mm you'd happily leave a 6mm in place as you've stated it is adequate in any situation?

Where is that in BS7671?

As far as I am aware there is no distinction between dwellings and non dwellings with regards to the sizing of the main bonding.
 
Where is that in BS7671?

As far as I am aware there is no distinction between dwellings and non dwellings with regards to the sizing of the main bonding.
Where did I state there was a distinction between dwellings and non dwellings in Bs7671?
I used an example of a non dwelling simply because it is highly unlikely that a 35mm bonding conductor will be required in any dwelling.
 
So lets say in a non dwelling setting the minimum (based on the supply N) required copper main bonding conductor according to BS 7671 for a TNCS supply is 35mm you'd happily leave a 6mm in place as you've stated it is adequate in any situation?

This thread is about work in a domestic dwelling installation and the guidance I mentioned also deals with this situation. I was trying to keep the advice relevant.
 

Reply to 6mm water bonding on PME in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock