Get an electrician in mate. He will advise you on the correct way to install such equipmentCan I run a 7.3Kw induction hob off of 2 x 16 amp circuits single phase I'm not sure what size cable is installed, I will check.
Would I be be able to run with the 2 x 16amp breakers or should I install a single 32 amp breaker with separate RCD?
Thanks in anticipation.
I will do so but I just wondered if the existing circuits were enough, other wise I will get a larger cable, which I can at least buy and run myself without paying electricians fees initially.Get an electrician in mate. He will advise you on the correct way to install such equipment
Many Electricians will not connect wiring which your have done and will insist on running it again themselves.I will do so but I just wondered if the existing circuits were enough, other wise I will get a larger cable, which I can at least buy and run myself without paying electricians fees initially.
But thanks for the reply
OH really, OK I suppose safety and regs come into play. Still doesn't answer my question regarding existing installation though. But thanks.Many Electricians will not connect wiring which your have done and will insist on running it again themselves.
The 2 x 16 amp feeds are on a single phase just separate breakers. Thanks for your reply.Running things dual phase is pretty unconventional over here
Hi James, thanks for the reply. I know that the electrician that installed the 2 circuits was providing for an electric hob which I think do run one set of of rings for each circuit. Should I ask for a single 32 amp breaker to be installed?as a general rule, a device shouldn't not be run from 2 different breakers unless they are physically interlocked so they trip together.
there are some exceptions but they are unlikely to come into play for your Hob.
Rings? I don’t think so!Hi James, thanks for the reply. I know that the electrician that installed the 2 circuits was providing for an electric hob which I think do run one set of of rings for each circuit. Should I ask for a single 32 amp breaker to be installed?
I still need to check the size of cable he has installed.
I'm basically wondering if the existing wiring will handle the load?
By Rings I mean ceramic hobs. But do they not run on separate circuits????Rings? I don’t think so!
Fairly common in my part of the country, where there are loads of two phase farm supplies, but agree that it's unconventional for a domestic supply.Running things dual phase is pretty unconventional over here
It's more likely to be one for oven and one for hob.The 2 x 16 amp feeds are on a single phase just separate breakers. Thanks for your reply.
Can I run a 7.3Kw induction hob off of 2 x 16 amp circuits single phase I'm not sure what size cable is installed, I will check.
Would I be be able to run with the 2 x 16amp breakers or should I install a single 32 amp breaker with separate RCD?
Thanks in anticipation.
The oven is on a separate breaker and the two other breakers are marked electric hob 1 and electric hob 2 . I need to pull out my cabinet to see where the cables/outlets are positioned and what size cable is provided. I have a feeling that there are two points and I wired into one of them for my gas hob ignition but that was 6 years ago so everything is a little hazy.It's more likely to be one for oven and one for hob.
Do these feed into separate switches/points ?
You still need to look at cables sizes.
He needs to get an electrician in.Using all 4 burners at max? probably never. With one 16a MCB and one circuit it will probably never trip. If it does but both cables into one 32A MCB making a ring of 1 point.
*Assuming there's nothing else fed from these 16a circuits, the cabling is the right size, and you have a suitable cooker outlet or cooker isolator. Not wiring two 13a plugs together.
put both cables into one 32A MCB making a ring of 1 point.
Fairly common in my part of the country, where there are loads of two phase farm supplies, but agree that it's unconventional for a domestic supply.
Unconventional doesn't make it wrong though, so I can't think of a reason to say it definitely shouldn't be done, although the MCBs should be a DP and the isolator a TP.
With one 16a MCB and one circuit it will probably never trip. If it does...
Should I ask for a single 32 amp breaker to be installed?
Completely and fully agree that gas is far superior for a hob, but a common reason for changing to electric is to avoid costly annual gas checks in rented property.And on another note, why would you change from a gas hob to an electric hob? Gas hobs are much nicer to cook on and cheaper to run.
Completely and fully agree that gas is far superior for a hob, but a common reason for changing to electric is to avoid costly annual gas checks in rented property.
Gas heating and water changed to electric or oil as well, although my experience is mainly with LPG rather than natural gas.
From a landlords point of view, electric oven and hob have benefits over gas both for, safety, and maintenance costs.Completely and fully agree that gas is far superior for a hob, but a common reason for changing to electric is to avoid costly annual gas checks in rented property.
Simple, just ask your electrician what they want you to order.@Taylortwocities not going to do it by myself.
Just want to know and check hows the cable will look like... and want to buy online material... work will be done by certified guy.
Bc I am currently in CzechiaThat’s your second opinion then.
When I was “on the tools” I hated customers who bought their own materials. Often it was just plain wrong, or some cheapo tat that wouldn’t last a week. Or it hadn’t arrived. All of these added to time on thd job, and cost the customer more ££.
On more than one occasion I’ve just walked out to another job.
Look, It’s a new circuit. You’ll need a registered electrician, he/she has trained for years, is competent and is assessed annually. Trust him/her, you won’t save any money.
Surely it's a three-phase supply there rather than a large single phase supply? You really need someone familiar with Czech wiring regulations and practices.Bc I am currently in Czechia
I do not trust these people at all.
I am not in west eu or US... So it's pain here. So many diletans and I can imagine how they are assessed :/
It would probably work fine on the single phase due to diversity if nothing else.He said i have 1phase 25A CB, and he said that my induction 7.3kw should work with it... that these are modern and know how to regulate power....
but he suggested that i should go for 2x 25A CB setup.
Confused.