Hi all , was doing a periodic on a domestic board. First I got 75V between the main earth and bonding earth . There was a L/E fault after clearing the fault I've tested between earths and now getting 8V. Is that acceptable , or is it still a fail .
Thanx in advance.
 
If your getting 8V then your bonding isn't very good.
 
Why do you not just test the bonding properly before making any decisions.
 
remake the clamps on clean copper. check the terminations. low ohms test MET to pipework.
 
If you had perfect continuity then you couldn't have a voltage between the two. I think you should check your continuity with a wander lead.
 
Between main earth and earth bonding cables at the board.
Didn't do continuity because was getting volts on earth. I was thinking could it just be transient voltage ? After all it's only 7V

The way I read your posts,you are disconnecting the bonding at the board and testing for voltage between a disconnected bonding cable and the earthing conductor (which is presumably is still connected to the system earth

What is your thinking behind carrying out this puzzling voltage test at first when a fault was apparent and later after the fault was cleared
Why was such a test carried out in the first place ?

A simple continuity test of the bonding conductors, yes,but what is your reasoning behind these voltage tests ?
 

Reply to 75 volts on earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
771
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
405
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
737
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock