mazo

hi,folks
i need some help
i have a 800amp main incomming over current switch with a bolt on earth leakage current relay,that seem to be tripping in bad weather ie when lightning is around,the site has 12 other sub boards none of which have the same device.
my question is does anyone else think it trips due to lightning feeding back up the system via earth .
the site has 2 very high lighting towers that may be conducting said unwanted voltage.
thanks guys.
mazo
 
whats its rating whats it set at have you done a rcd ramp test yet, and yes lighting can cause nuisance tripping but not regular as you suggest unless something local is acting like a lightning rod.
 
is this the only earth leakage current device in the system? What other sub supplies are down streanm?
 

Reply to 800amp main switch in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock