W

Welshsparky

Got a customer that doesnt want a 6mm shower cable upgraded to 10mm but rather downgrade her shower to 8kw

Anybody know were to find a decent not to price 8kw shower?
 

telectrix

Scouser and Proud.
Respected Member
Forum Mentor
Electrician's Arms
CCTV / Alarms
Solar Guru
Trainee Access
DIY
B&Q, screwfix. cpcfarnell. ebay.
 
S

Spazz

You can use 6mm cable on a 8.5kW shower if the cable is direct clip with no installation.

Otherwise try the ones above

Personally anything above 8.5kW I try and push them to upgrade their cable
 
P

Plonker 3

As long as the OCPD is correctly rated for the cable, then I think you could get away with a 8.5kw as they are highly unlikely to use the higher temperature settings unless they like to scold themselves.
 

electromonkey

Electrician's Arms
What's the cable run and cable condition? Depending on the distance and installation method then a 9.5kw could be run from it. Providing it's on a 40A mcb.
 
P

PC Electrics

What is the installation method of the existing cable?
And its approx length?

These are the first questions to answer when assessing the adequacy of a circuit.

If it's not installation method C, then can you change it to C? for example by lifting the cable out of insulation where it runs through the loft?
 
S

Swicade

If the supply cable goes through the loft at all i personaly wouldn't fit any shower above 8.5kw on a 6mm at all (even then it could be very tight depending on cable length.

My main reason for this stance these days is because i've been in that many lofts in the last few months which have had extra insulation installed (due to government schemes for free insulation) that gets thrown over all cable's and joists (so you cant see the joist just have to feel for them) that a cable close to the limit will soon be unsuitable through external influences. Not our problem some will say but if it all melts/catches fire who the first person they're gonna blame?....muggin 'ere and i could do without that hassle tbh.
 
S

SirKit Breaker

If the supply cable goes through the loft at all i personaly wouldn't fit any shower above 8.5kw on a 6mm at all (even then it could be very tight depending on cable length.

My main reason for this stance these days is because i've been in that many lofts in the last few months which have had extra insulation installed (due to government schemes for free insulation) that gets thrown over all cable's and joists (so you cant see the joist just have to feel for them) that a cable close to the limit will soon be unsuitable through external influences. Not our problem some will say but if it all melts/catches fire who the first person they're gonna blame?....muggin 'ere and i could do without that hassle tbh.
Very good point............

Cheers...........Howard
 

i=p/u

Electrician's Arms
CCTV / Alarms
has length really got anything to do with this question. as volt drop and zs is only factors to do with length.

but please teach me something if it works.





What is the installation method of the existing cable?
And its approx length?

These are the first questions to answer when assessing the adequacy of a circuit.

If it's not installation method C, then can you change it to C? for example by lifting the cable out of insulation where it runs through the loft?
 

Guitarist

Electrician's Arms
DIY
As long as the OCPD is correctly rated for the cable, then I think you could get away with a 8.5kw as they are highly unlikely to use the higher temperature settings unless they like to scold themselves.
Unless it's a really hot summer, I don't know of anyone who uses the "low" setting on an electric shower. Remember, fixed output, variable flow :)
 

darkwood

Super Moderator
Staff member
Super Moderator
Moderator
Forum Mentor
Electrician's Arms
CCTV / Alarms
Trainee Access
has length really got anything to do with this question. as volt drop and zs is only factors to do with length.

but please teach me something if it works.
You Kind of answered your own question, if length is too long for the given size and loading of the cable then volts drop may not comply with reg's
 

trev

Regular EF Member
Just suppose you did a rewire, you did all the calcs and derated the cable accordingly and have the paperwork to prove it.Everything is fine and tests out perfectly so you cert it, money changes hands and everyone is happy.
Then some muppet comes along and dumps 200 mm of tickly wool all over it which causes the cable to heat up and eventually starts a fire.
Who is going to be held responsible? Certainly not you imho, you have done your job correctly and can prove it. What I think the problem is is that companys have sprung up out of nowhere supplying insulation all paid for by the government. If they are not aware of the effect of their product or are unable/unwilling to train their monkeys oops sorry I meant installers then it's their look out not ours.
 

darkwood

Super Moderator
Staff member
Super Moderator
Moderator
Forum Mentor
Electrician's Arms
CCTV / Alarms
Trainee Access
I agree trev but with hind-sight now all buildings that dont have loft insulation are slowly been upgraded and all new have it, if you wire through the loft you should be designing with the propect of loft insulation been fitted at some future point, i just did one and kept the cable above and where it passes down i fixed a 2"/2" trunking so any depth insulation would be kept off it.
 
Status
Not open for further replies.

Electrician Talk

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Electrical 2 Go - Electrical Supplier and Electrical Wholesalers
Electrical Insurance
ElectriciansForums.net (formerly known as ElectriciansForums.co.uk) was setup in April 2006 to provide free electrical advice to both professional and DIY electricians. Whether seeking advice for auto electrics, trying to find electrical installation condition reports (EICR) form downloads, or whether you're here just to talk to other electricians; we've been a first-choice website for tens of thousands of sparkies for well over a decade.
Top