Hi ,

I'm getting electrician to change my consumer unit and was planning to get :

it has 2 x 80a 30ma Type A RCD's

but for shower it says -
500 (9.5kW)41.345A10mm2RCBO

will this 80a fuse not be like overload or something? Do i need to buy 40-45A fuse?
 
An RCD is not a 'fuse'. 80A is its maximum load, and the sum of the MCBs running from it must not add up to more than 80A, unless your DNO fuse is 80A or less.
Following on from another thread I've just posted on, is the shower rated at 9.5kW @ 240V or 230V?
 
An RCD is not a 'fuse'. 80A is its maximum load, and the sum of the MCBs running from it must not add up to more than 80A, unless your DNO fuse is 80A or less.
Following on from another thread I've just posted on, is the shower rated at 9.5kW @ 240V or 230V?
Shower info - A Power Input of 240 V and 40 amp circuit breaker is required for max output ( 9.5 KW )

in simple words ,if i buy that consumer unit ,will i need to buy any extra wylex fuses or what is there included is good enough?
 
The standard UK voltage is 230V, not 240V, so your shower is rated at 8.275kW in reality. The 9.5kW is marketing.
The current drawn by this will be around 36A, so yes, you do need to buy a 40A breaker AND, the sum of the breakers on the side of the CU you fit this must not add up to more than 80A, unless you can confirm that your DNO fuse is not more than 80A.
 
The standard UK voltage is 230V, not 240V, so your shower is rated at 8.275kW in reality. The 9.5kW is marketing.
The current drawn by this will be around 36A, so yes, you do need to buy a 40A breaker AND, the sum of the breakers on the side of the CU you fit this must not add up to more than 80A, unless you can confirm that your DNO fuse is not more than 80A.
ok got it! so something like this?will this be compatible with that consumer unit?

 
Why is your electrician not specifying what board and protective devices you need?
 
Not any more.
According to the BEAMA guide that somebody posted the other day, it is. We never fit split load boards but according to this documant diversity IS taken into account when selecting and erecting.

If you have more upto date info can you share please?
 
I'm now retired from active contracting, so do not posses a copy of the 18th, although I try to keep up to date with changes from the 17th.
My information comes from recent previous posts on here, and as I understand it, it's a recent change.
 
According to the BEAMA guide that somebody posted the other day, it is. We never fit split load boards but according to this documant diversity IS taken into account when selecting and erecting.

If you have more upto date info can you share please?
Hi. It was me that posted the BEAMA document.
Apparently there is a 2 stage process when applying diversity to a group of circuits protected by an RCD.
Stage 1 work out and apply diversity.
Stage 2 read manufacturers literature.

Excerpt from BEAMA document:

"Conclusion
The minimum rated current Inc of the circuit in the consumer unit for the RCCB
(A) based upon diversity is 78.4 A. However, overload protection shall not solely be
based on the use of diversity factors of the downstream circuits, see Regulation
536.4.202. To achieve overload protection of the RCCB circuit, the rated current of
the OCPD shall be selected according to the manufacturer’s instructions
, which for
BEAMA members, is coordinating with the upstream OCPD, in this case a 100 A fuse.
Therefore, the required minimum rated current Inc in the circuit of the consumer unit for the
RCCB (A) is 100 A."


So, overall, not much point in calculating the diversity?
 

Reply to 9.5kw electric shower in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
715
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
645
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock