Hi every one,
I should know better but can’t get my head round this one and lost my notes from College.
On site guide is saying up to a 9.7Kw shower the cable CSA should be 16mm this seems rather high to me and impossible to work with.
I am fitting a 9.5Kw shower and looking at smaller CSA than 16 probe’s 10 but this will be for an assessment for a company and has to be correct can some one give me the formula for CSA, the fuse to be used are 40Amp and the total run is 11Meters from consumer unit to the shower.

Thanks Ian.
 
Not that your 9.7kW shower is likely to trip it but your shower is theoretically pulling 42A so having it on a 40A breaker doesn't look too good for an assessment. Haven't got any books with me but 6mm clipped direct has a surprisingly high CCC. :)
 
Thanks for your feedback any more please feel free Thanks Ian.
Electricians guide page 52 under : Upto 9.7Kw Shower and thanks i will find my paper work some where prob's in a cupboard
 
Hi and thanks for replying the run is up about 50mm on plastick trunking behind fitted kitchen unit and then to the loft space, this has from what i am told heavey duty lagging but will run over top and then down into a cupboard for switch D/Pole.

I was looking closer at the On site guide and found like a nut i was looking at all the wrong tables untill i got the correct one and i have used Clipped direct method. 2.5 has a 27Amp CCC i am calculating 10 mm should be ample for a 11M run

Thanks Ian.
 
Loft insulation there is and lots of it so i will run it over the top, This is a bungalow i am working in.


Thanks for reply
 
I was looking closer at the On site guide and found like a nut i was looking at all the wrong tables untill i got the correct one and i have used Clipped direct method. 2.5 has a 27Amp CCC i am calculating 10 mm should be ample for a 11M run



I did say I thought you had the wrong table!!! Still wanted to see you terminate 16mm in to a pull cord... that would have been worth watching!!!

Are you "In" currently Ian.... I'll pop round as I'm headed "up the road"!!
 
On the basis you're going to use 10mm cable and that you will be using a pullcord isolator switch, I'd highly recommend the Crabtree 50A isolator.
 
As per Instructions with the shower a 40A fuse is to be used.

Thanks Ian.

As Pushrod has already stated, wouldn't you be better sticking to the regs and using a 45A fuse, rather than following what seems to be the wrong advice in the instructions included with the shower ?

Although the shower manufacturers are probably selling the product as a 9.7Kw unit when in actual fact it is much less :innocent:
That is probably why they are advocating a 40A protective device. Either that or they are numpties.
 
As Pushrod has already stated, wouldn't you be better sticking to the regs and using a 45A fuse, rather than following what seems to be the wrong advice in the instructions included with the shower ?

Although the shower manufacturers are probably selling the product as a 9.7Kw unit when in actual fact it is much less :innocent:
That is probably why they are advocating a 40A protective device. Either that or they are numpties.

Some manufacturers still use 240V instead of 230. The shower is probably rated at 9.5Kw at 240V. 9500 ÷ 240 = 39.6A.
 

Reply to 9.5Kw Shower on-site guisde? 16mm Twin & cpc? in the Australia area at ElectriciansForums.net

Similar Threads

Run into this today at a house my nephew is moving into.... Original Dolphin 860 Shower (8600W) installed on 6mm Twin and Earth - maybe 15m...
Replies
4
Views
4K
ELECSA Certification Scheme Regulations Clarification (ELECSA Assesment)
Hi All, I have my ELECSA assessment in a few weeks time. I was going to install an in-line water heater at a friends house but am now considering...
Replies
73
Views
9K
As you may know looking at some of my posts I've been thrown back in the deep end recently – and don’t have much experience with complicated...
Replies
9
Views
4K
Another long one from me ... I hope that it covers all the bases and is a more thorough approach to the subject. It is my first design work so...
Replies
44
Views
6K
B
Hi Guys, Looking for a little advise regarding installation of new supply to feed a communal shower block at a local Girl Guides Camp. The owners...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock