Discuss A close shave! in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,578
Today I was at a customers house (domestic) to do a simple light change.

I turned the existing light on, went down stairs and turned what I thought would be the correct breaker off. I went back up the stairs and the light was off. I never take it for granted that that is the correct breaker so I tested with the meter as well. It tested as dead and I was about to start removing it.

The customer then came up the stairs and asked me why I'd switched off all the power rather than just the lights, I thought I had perhaps tripped an RCD. Went back to the CU and the RCD was still up, yet all power was off.

So... Whilst I had been walking back up the stairs after switching the breaker off they had had the power cut in the street! This has never happened to me before and I'm just wondering if I made any errors in my safe isolation procedure which could have avoided this? I can't see how I could have though. Luckily it was the right circuit breaker but that is besides the point. Bit scary!
 
Today I was at a customers house (domestic) to do a simple light change.

I turned the existing light on, went down stairs and turned what I thought would be the correct breaker off. I went back up the stairs and the light was off. I never take it for granted that that is the correct breaker so I tested with the meter as well. It tested as dead and I was about to start removing it.

The customer then came up the stairs and asked me why I'd switched off all the power rather than just the lights, I thought I had perhaps tripped an RCD. Went back to the CU and the RCD was still up, yet all power was off.

So... Whilst I had been walking back up the stairs after switching the breaker off they had had the power cut in the street! This has never happened to me before and I'm just wondering if I made any errors in my safe isolation procedure which could have avoided this? I can't see how I could have though. Luckily it was the right circuit breaker but that is besides the point. Bit scary!
Lucky then HHD
 
I'm just wondering if I made any errors in my safe isolation procedure
no, if you have isolated it then you have done it , never rely on a neon screw driver ,lol..
me if I done it it all the lighting mcb would be off you never know ,,what is feeding what .or islotate the full sysem .there is no good spark a dead one .
 
no, if you have isolated it then you have done it , never rely on a neon screw driver ,lol..
me if I done it it all the lighting mcb would be off you never know ,,what is feeding what .or islotate the full sysem .there is no good spark a dead one .
Lots of good Sparks about HHD!!
 
You missed out the final step of the safe isolation procedure, to wit to check your approved voltage tester is still functioning correctly after you have proved the circuit you are working on is dead.

Of course you also prove it is working before testing a circuit.

Someway to go before you can be an AP. ;)
 
Last edited:
Ha, reading your original post HHD I thought you were going to say Customer had flicked it back on while trying to sort out his lack of appliance power. Faced with a DNO outage I would flick the main switch, pronto. What would really make your day is when the network supply is re-energised there might be a surge and it blow up the boiler control board or some such ... “that was you that dun that” says the Customer.
 
Last edited:
I’ve had that before....but it was one phase out which sounded like BS when I was trying to explain to the customer.

I had a real rollocking off a business owner asking why i had turned all power of in the building without permission . She would not believe that it was coincidence an electrician was in the building during a power cut .
 
I was swapping a light fitting in a garage, isolated the circuit but it was quite dark but enough light to see.

I just touched a terminal with my screwdriver and there was a flash and an almighty bang. So I’m stood on my steps wondering why I’m still upright and what had just happened.

Then I heard the rain bouncing off the roof. Lightning stoke was two streets away.

Luckily the poo stayed on the inside but only just... ?
 
I'm confused...not that it takes much these days...
If you check your approved voltage tester is working, then you isolate the circuit and test it and it's dead, then you check your tester again on a known source and it doesn't light up. either the tester is faulty or the test circuit is dead, and if that's not the circuit you thought you had switched off then maybe it's a power cut like HHD had? But if you tested on a proving unit then you would get an ok test, so that wouldn't tell you that there was a power cut in the street...
 
Nearly as good as a power cut ,
believe you've successfully isolated correct circuit
,now triggering a N-E event.
,but actually triggered a remote RCD .. that some one will reinstate in a few minutes !
.... worry not only my paranoia at work ....
 
A habit I got in to as an apprnetice, and still do most of the time, when trying to work out which mcb feeds something I'll switch the MCB on and off a couple of times to make sure the right circuit goes on and off, then proceed to lock off etc.
 
Just disconnecting the line does not isolate a circuit. To isolate a circuit all live conductors (Ls and N if used) must be disconnected from the source of energisation. A single pole MCB is a functional switch not an isolating switch. Isolation requires a minimum air gap between the energised contacts and circuit contacts dependent on the applied voltage and a secure way of locking off.

One checks for energisation on the supply side (which confirms the Approved Tester is working at the circuit voltage) and then on the circuit side of the closed isolator. Then one opens the isolator to isolate the circuit from the source of energisation and checks for energisation on the circuit side and then the supply side to demonstrate de-energisation of the circuit side. The evidence of isolation is de-energisation on the circuit side and energisation on the supply side tested in that order.

The case of de-energisation on both sides of an isolator does say anything about disconnection or de-energisation of the circuit because for multifarious reasons the source of energisation may have temporarily disappeared ie: a power cut.
 
Last edited:
My safe isolation procedure includes proving you have identified the correct circuit, motor, pump or what ever is to be worked on. This can be difficult some times but in this instance a couple trips between the MCB and the light circuit using the approved voltage tester should of been sufficient (this can be made much simpler if there are two of you).
 
Just disconnecting the line does not isolate a circuit. To isolate a circuit all live conductors (Ls and N if used) must be disconnected from the source of energisation. A single pole MCB is a functional switch not an isolating switch. Isolation requires a minimum air gap between the energised contacts and circuit contacts dependent on the applied voltage and a secure way of locking off.

One checks for energisation on the supply side (which confirms the Approved Tester is working at the circuit voltage) and then on the circuit side of the closed isolator. Then one opens the isolator to isolate the circuit from the source of energisation and checks for energisation on the circuit side and then the supply side to demonstrate de-energisation of the circuit side. The evidence of isolation is de-energisation on the circuit side and energisation on the supply side tested in that order.

The case of de-energisation on both sides of an isolator does say anything about disconnection or de-energisation of the circuit because for multifarious reasons the source of energisation may have temporarily disappeared ie: a power cut.
What you are saying does make sense Marconi but BS7671 does state that a circuit breaker to BS 60898 (I.e a standard mcb) can be used as a form of isolation. See table 53.4 BGG.
Apologies for not quoting the BBB but I am out and only have the BGB to hand.
 
I have had similar. Was running in new sockets in an office and was second fixing the faceplates when suddenly it went pitch black. I stupidly assumed (as slightly panicky at the time) I tripped something despite the new circuit cable not being connected to the board yet! With the alarm blasting and in relative darkness I fumbled about trying to suss out what had happened. It was only after a couple of mins that I realised the street lights and other premises were all off too..!

The answer in my mind would be to check live, check dead, check live again and check dead again..
 

Reply to A close shave! in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock