Hi all,

I'm new to this forum and its due to the fact that I have my AM2 exam this coming Monday.
I just have a few questions.
- Do I need to earth bond the cable tray?
- I know that the External Loop Impedance Test is on the incoming side of the installation, and that when testing i need to disconnect the main earth from the earth bar to test. The board is a 3 phase and so do I need to test between L1-N-E L2-N-E and L3-N-E or do I just take a reading between each phase and earth then obviously record the highest reading?
- For the insulation resistance testing am I right in thinking that;
- I need to disconnect the RCBO and the fly leads completely from the CU?
- Disconnect the Lighting circuit and remove the lamps so that i can test the circuit when operating the switches?
- Disconnect the incoming supply for the CU to my motor contactor and place in push in terminals so that I dont damage the contactor?
- Disconnect the load from the unswitched fused spur for the co2 detector?
Then do a global test for the rest of the circuits at the main switch? i.e L1-L2 L1-L3 L3-L1 L1-E L2-E L3-E? Or go across each circuit individually at the cu?

Anyway thats enough so far that I can think of. Any help would be fantastic!

Cheers,
Tom.​


 

Reply to A couple of AM2 questions. in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi all, hoping for some advice, I’ve recent resit my AM2s after failing on first attempt… I’ve passed all my resit apart from section C just on...
Replies
0
Views
831
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
416
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
426
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
653

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock