Discuss A little help regarding fire detection system... in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

E

Eddiesparks

Some help from someone that knows a bit more about fire detection systmes than me please!

I am rewiring a pub (FOR MY SINS!) with what i think is classed as an HMO above (one bathroom, one kitchen - four seperate rooms with individual tenants in each) and they have asked (late in the day i may add!)for a fire detection system. The only info I got from them is that the fire risk assessment people have asked that the system s interlinked between upstairs and downstairs which is fine to do. So basically, for the HMO (all on one storey) it looks as if I need a grade D LD2 system with a smoke in the hallway between rooms (providing it is no greater than 7.5M to any bedroom door) and a heat in the kicthen. Is this right?!

Also what do i need in the pub? It is not huge but there is a kithcen and cellar so I'm thinking a heat in kitchen and smokes in cellar and in two or three zones of the pub. I'm used to simple house bashing - a smoke upstairs and downstairs and a heat in kitchen, mains feed, linked with third core of 3 core and E and with battery back up!!

Also - Could I get away with using interlinked by radio signal smokes/heats fed by various lighting circuit's perm lives and neutral?! I know this is allowed on domestic (I learn it from a booooook) The place is finished (most of my work is yukky surface mounted, not much job satisfaction from this one!!) and it would be loads easier if i could get away with not runnign three core between all the smokes and heats!

thanks everyone
 
Bombs coming Murdoch.....!!!
A pub is classed as commercial premises, so will require a full fire alarm system, Control panel etc. And the flat being HMO, you can interlink mains detection with a fire alarm panel, but if your going to install a new system, you might as well install the complete building.
 
If it were me, as someone not qualified in fire alarm deign, I would get someone who was to design and commission such a project for me and keep my own mind free to concentrate on the rest of the rewire.
 
Oh dear oh dear, This is not a job for a Domestic installer, get an electrician in and quick before you get yourself into a hole you cannot escape from.
 
My advice is to get a professional to design the system, price it and then show the client. I usually get my alarm company who I use a lot to design and issue me with a drawing, I allow for first fix and all cabling, they allow for supply of all kit, they also 2nd fix and program the panel, they also take the maintenance contract on and do the client training, I add 15% onto their costs and pay them via my books so I still get a cut. They take responsibility and look after the installation and customer for years after with no come back to me and no hassle, it is a specialist job IMO and needs to be left to the professionals not a Domestic Installer.
 
My advice is to get a professional to design the system, price it and then show the client. I usually get my alarm company who I use a lot to design and issue me with a drawing, I allow for first fix and all cabling, they allow for supply of all kit, they also 2nd fix and program the panel, they also take the maintenance contract on and do the client training, I add 15% onto their costs and pay them via my books so I still get a cut. They take responsibility and look after the installation and customer for years after with no come back to me and no hassle, it is a specialist job IMO and needs to be left to the professionals not a Domestic Installer.

That there is pretty much the model way to do it, I put in some really big systems, we have an fire partner, we contract to them as install contractors, the provide us with design, supply and commission services providing us access to so pretty nifty managed protocol systems.

I get them out of the mire, regularly, they bend over backwards to help me, it's a win win situation
 
That there is pretty much the model way to do it, I put in some really big systems, we have an fire partner, we contract to them as install contractors, the provide us with design, supply and commission services providing us access to so pretty nifty managed protocol systems.

I get them out of the mire, regularly, they bend over backwards to help me, it's a win win situation

Without this partnership with electricians, we would have no business, In return, they get on the council list, so they gain aswell
 
ok boys fair enough I think that was what i was asking, is it do-able by me or do i need a specialist. Obviously out of my league

I will most likely just tell him it is not my domain and get him to call a fire alarm company himself, not too fussed about the 15% I am just really keen to get out of that job and onto the next as quick as poss! Not loving it to be honest!
 
Eddie, Unfortunately mains smokes are not permitted in commercial premises, they are only suited to domestic dwellings, and 2 level HMO.
If you feel its out your safe zone, team up with a local fire alarm installer, were they design, you install and charge for all the cabling, they come back, commission and sign off.
 
Some help from someone that knows a bit more about fire detection systmes than me please!

I am rewiring a pub (FOR MY SINS!) with what i think is classed as an HMO above (one bathroom, one kitchen - four seperate rooms with individual tenants in each) and they have asked (late in the day i may add!)for a fire detection system. The only info I got from them is that the fire risk assessment people have asked that the system s interlinked between upstairs and downstairs which is fine to do. So basically, for the HMO (all on one storey) it looks as if I need a grade D LD2 system with a smoke in the hallway between rooms (providing it is no greater than 7.5M to any bedroom door) and a heat in the kicthen. Is this right?!

Also what do i need in the pub? It is not huge but there is a kithcen and cellar so I'm thinking a heat in kitchen and smokes in cellar and in two or three zones of the pub. I'm used to simple house bashing - a smoke upstairs and downstairs and a heat in kitchen, mains feed, linked with third core of 3 core and E and with battery back up!!

Also - Could I get away with using interlinked by radio signal smokes/heats fed by various lighting circuit's perm lives and neutral?! I know this is allowed on domestic (I learn it from a booooook) The place is finished (most of my work is yukky surface mounted, not much job satisfaction from this one!!) and it would be loads easier if i could get away with not runnign three core between all the smokes and heats!

thanks everyone
Emergency lighting, a nurse call system in the disabled toilet, dedicated supplies to the cellar equipment, probably seperate Distribution board for kitchen equipment, gas valve linked to fire alarm panel, Car park lighting, satellite tv system, supplies for drinks chillers, Garden Lighting, Multi gang switching for general Lighting, Full fire alarm system, network supplies for telephone and internet system, supplies for fruit machines, supplies for glass washers, general sockets for cleaners, supply for central heating system, supplies for automatic flushes for toilets, neon signage supplies and I will add to the list should something pop into my head.

Mike
 
Emergency lighting, a nurse call system in the disabled toilet, dedicated supplies to the cellar equipment, probably seperate Distribution board for kitchen equipment, gas valve linked to fire alarm panel, Car park lighting, satellite tv system, supplies for drinks chillers, Garden Lighting, Multi gang switching for general Lighting, Full fire alarm system, network supplies for telephone and internet system, supplies for fruit machines, supplies for glass washers, general sockets for cleaners, supply for central heating system, supplies for automatic flushes for toilets, neon signage supplies and I will add to the list should something pop into my head.

Mike

Gas valve also needs to be linked into the extraction system over the cookers, if the extraction is off then the gas won't operate.

I normally use the fire alarm to shut down all air handling plant, including the kitchen extract!. Which then shuts the gas down, saves on interfaces lol
 
This has been an interesting read.

Having only ever worked on kilns and furnaces, fire detection didn’t really figure in the scheme of things. Although some Muppet suggested we had them fitted. Could have been interesting.
 
This has been an interesting read.

Having only ever worked on kilns and furnaces, fire detection didn’t really figure in the scheme of things. Although some Muppet suggested we had them fitted. Could have been interesting.

I can imagine some of the responses;

"FIRE",, Yes correct we've got plenty of it.

"Smoke,, somethings burning", Yes, you're not wrong there, usually comes with all the Fire we have.
 
Gas valve also needs to be linked into the extraction system over the cookers, if the extraction is off then the gas won't operate.

I normally use the fire alarm to shut down all air handling plant, including the kitchen extract!. Which then shuts the gas down, saves on interfaces lol
Ah yes thats very true a fresh air fan needs to be running as well as extract as you mentioned, quite right.
 
Ah yes thats very true a fresh air fan needs to be running as well as extract as you mentioned, quite right.

Good point mike!

We have to interlock extraction Canopies because of the gas regs, in complete madness the gas regs do not call for the intake to be interlocked too!, however like mike I use dual pressure switches and interlock both!!.

And all air handling is normally interfaced to the fire alarm normally on the roof or plant room
 
This has been an interesting read.

Having only ever worked on kilns and furnaces, fire detection didn’t really figure in the scheme of things. Although some Muppet suggested we had them fitted. Could have been interesting.

I can just imagine some health and safety nob, standing with a standard smoke head in his had looking at a 40m ceiling above a ladle lol..........

In seriousness super aggressive environments like a foundry would have a fire risk assessment these days that would call for manual detection only and the need for automatic detection being negated with the exception of the office and public areas such as reception. So by modern day standards just manual call points dotted around on the foundry floor, protected with compliant covers and call points on every final exit.

It's not uncommon, we did a run of bus garages a few years back, L5 system, no automatic detection within the bus parking garage die to diesel smoke, just MCP's and sounders, and in the pit area, linear heat cable.
 

Reply to A little help regarding fire detection system... in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
289
I'm about to order this wired smoke alarm system as it can network but I just went to see how my existing fire alarms are hooked up and there...
Replies
12
Views
1K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
983
Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Replies
3
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock