When testing Ze on a TT the only connection between the line and the earth rod is the actual ground.

When you do a Ze is it actually sending a small current through the actual ground from the earth rod at the house to the earth rod at the transformer?

Also, related to the above, I have 2 separate garden light circuits. The customer complained of RCD tripping. The garden lights have junction boxes buried in the ground that lead on to the next light. These Jb's are full of water hence the tripping (IR results 0.006Mohms N-E).

With regards the above paragraph I am getting 0.15Mohms between the Neutrals of both separate garden light circuits (also the earths and line's but you would expect that as light bulbs are in and 0.006Mohms N-E). This is with all the conductors completely isolated, is this again because the separate circuits have a link via the actual ground (due to all the water in the buried JB's)?
 
Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #3
You must be logged in to see the message.
 

Ian1981

-
Mentor
Arms
Esteemed
You must be logged in to see the message.
 

DPG

-
Arms
Esteemed
You must be logged in to see the message.
 

telectrix

-
Mentor
Arms
Esteemed
You must be logged in to see the message.
 

edexlab

-
Arms
You must be logged in to see the message.
 

Lucien Nunes

-
Mentor
Arms
Esteemed
You must be logged in to see the message.
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members

Reply to A question about how current travels through the real earth? in the Electrical Forum area at ElectriciansForums.net

Top Bottom