I am still in the training process. I have one question if anyone can help thatll be great.
My question is when carrying out continuity test on a radial circuit I know we have to link. When linking can we just link between the main Earthing terminal and circuit breaker? or does it have to be the exact cpc for that circuit and CB?

Many Thanks
 
for measuring R1+R2, you would measure just the cable concerned. link the L and cpc of the cable at CU, then measure at points. furthest point is your recorded result.
 
No you can put a link between the earth bar and MCB outgoing side. Sometimes it isn't possible to properly identify the correct cpc (eg when wired in singles)
 
Best practice, and if you can identify the correct cpc would be to remove the CPC and R1 from the board, link and measure at the end. This way you shouldn't have any parallel paths.
 
I know that I have to disconnect the main earthing and bonding conductor to avoid parallel paths. So is it accurate to just link between the CB for the circuit and the Main Earthing terminal , as MET has too many cpcs?

Thanks again.
 
If you can get your hands on a copy of guidance note 3 you will find it invaluable.
It's not overly expensive and is very clear.
The copy I have even has a pictures showing how to do the tests.
GN3, pre amendment advised Dillbs method but if I remember correctly for the 2391 tel and murdoch's method is the correct one and dillb's method was not advised.

go figure lol :rolleyes2:
 
p32 GN3.
It advises the use of a temporary link between line of the cct and the cpc bar.
When I did the 2391 we were told not to use the temp link but to use the cpc and line conductor connected together.

As far as I'm aware you remove the main earth for a Ze test to eliminate parallel paths but this is not necessary for R1+R2
 

Reply to A silly questions on Countituy testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
823
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
652
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
797
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
567
So I’m an apprentice and I’m just trying to get a better understanding of the science behind this because the electricians who have said it have...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock