A strange one :- replaced an inline mixed flow timer fan like for like yesterday. When powered on at the 3 pole isolator switch the fan was running at 25% speed and the shower light 12v halogen bulb was lit but very dim (note the pull switch for bathroom lights was off) All other bathroom downlights were off. When bathroom pull switch was turned on Both fan & shower light went off, bathroom downlights worked correctly.

All wiring correct on check. Checked 3 pole isolator loose neutral connection found. Retightened everything working as normal.

trying to work out why this would cause the fan to run slowly/dim downlight any ideas much appreciated.
 
If the new fan ran slow and caused the shower light to be dim, then the fan must have been in series with the light via the loose neutral.
Was the light neutral looped from the isolator?

Also was the old fan running slow, suggesting there was nothing wrong with it apart from a loose neutral?
 
Probably correct to assume that the loose neutral was present or may have got worse leading to the failure of the old fan and downlight transformer. At time of replacement both 12v shower light and fan were not working at all. Fair to say that due to the new fan and light showing problems as above, before fault correction, shows that the cause of fan and transformer failiure may well have been the poor connection of the neutral conductor
 
Impossible for me to now say if the loose neutral connection was the only fault and the fan/light transformer were not actually faulty. It could have been, fortunately, for the customer, they wanted a more powerful mixed flow fan fittng anyway.
 

Reply to a strange Slow running Manrose MFT100T in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
8K
Hello, I currently have two switches in my bathroom. One controls the lights above the sink and the other controls a light above the toilet and...
Replies
0
Views
731
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
989
Hi, I've just had some electrical work completed in the bathroom; I've recently refurbished the bathroom, replacing the old electric shower with...
Replies
39
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock