Reported fault was RCD tripping.

Another spark had been out and reported a Neutral fault on a ring circuit. As poewr could not be left off he removed the RCD (single RCD 7 way CU) and replaced it with a mains switch.

When I arrived there were two "ring" circuits in the CU one on a B32 and one on a B10.

Niether were rings however all IRs were in the high 100sMOhms at 500V, including to MET. So no fault evident.

Found the legs of one ring which had been mixed up in the CU and reinstated to an RCBO, could only find one accessory on the ring which had a spur to an outside socket, all tested ok and RCBO holds.

The two remaining cables had no ring continuity at all, found one accessory on one cable and this only had one feed in, again this tested ok and was reinstated to am RCBO and held.

At this point all expected power was back on with one ciruit still disconnected from the board.

This cable tested fine for IR but no accessory could be found to peform any other testing so was left disconnected.

Fully expecting to be back to rewire the faulty circuit but will at least kkow which one is faulty.

I would be interested to know how others would have approached this one.
 
from what you say, you done it logically.' and, more importantly, made it safe by the use of rCBOs.
Cheers Tel, its one of those where you leave thinking Ive been here most the day, fitted a new board with RCBOs yet the customer has still, in all likelihood, got the fault.

As you say it is safe now being on RCBOs.

If/when it trips again we'll at least know which circuit its on.
 

Reply to Absolute Nightmare fault. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
446
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
844
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
267
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
997
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock