Hi,
I am a DIY person (ie. not a qualified electrician) so I am sure this is a basic question but please bear with me.
I am looking to add a socket to the garage. I was looking at various online resources on how to wire this up and came across many videos and articles that said that if you are adding a spur off a socket in a ring circuit, you can only have one, not two spurs. The reason being that if two double spur sockets were added (in series), then the total load could be 52A (13A x 4), which would overload 2.5mm cable between the socket in the ring and the first spur.
OK I get that but isn't the whole ring circuit protected by MCB rated at 32A anyway, so way before you get to 52A, the MCB would trip? Also I understand that 2.5mm cable is rated at around 25A so even if you have one double socket spur, you could overload that piece of cable (between the socket in the ring circuit and spur) by plugging in two 13A appliances.
Or is it that,
1. Plugging in two 13A appliances would create 26A but it is just about at the max rating of 2.5mm cable so it's fine.
2. Since MCB is 32A, there is a range between 25A - 32A, which would overload the cable between the socket and the first spur, while MCB will not trip.
Can someone explain to me the thinking behind this?
Thanks.
I am a DIY person (ie. not a qualified electrician) so I am sure this is a basic question but please bear with me.
I am looking to add a socket to the garage. I was looking at various online resources on how to wire this up and came across many videos and articles that said that if you are adding a spur off a socket in a ring circuit, you can only have one, not two spurs. The reason being that if two double spur sockets were added (in series), then the total load could be 52A (13A x 4), which would overload 2.5mm cable between the socket in the ring and the first spur.
OK I get that but isn't the whole ring circuit protected by MCB rated at 32A anyway, so way before you get to 52A, the MCB would trip? Also I understand that 2.5mm cable is rated at around 25A so even if you have one double socket spur, you could overload that piece of cable (between the socket in the ring circuit and spur) by plugging in two 13A appliances.
Or is it that,
1. Plugging in two 13A appliances would create 26A but it is just about at the max rating of 2.5mm cable so it's fine.
2. Since MCB is 32A, there is a range between 25A - 32A, which would overload the cable between the socket and the first spur, while MCB will not trip.
Can someone explain to me the thinking behind this?
Thanks.