Hi

Just a quick one, I am a qualified electrician but i haven't been on the tools for a while and won't be doing the work but just trying to help a friend out.

Basically they are having a new kitchen diner and they currently have gas hob and small single oven which are fed off the ring main. They are wanting an electric induction hob (7.2kw) and combination oven (3kw) so i said they would need 2 new separate circuits for these.

However they have no spare ways in their DB (older style 6 way DB with RCD) ideally they would need a DB upgrade but in the past someone has installed the combi's boiler in front of it (amazing) and can only just get in turn reset an MCB.

But they have 100A main fuse with 25mm tails that is split already one to the main DB and one to 60A large switch that has a 45A fuse in that just has the garage SWA supply to it, my question is it just possible to replace this 60A switch to a small 4/5 way DB single RCD that will house garage supply (down rate to 20A) Hob circuit (40A) and Oven circuit (20A)

All advice and options welcome

Thanks
 
is it possible to replace 60A switch with a new consumer unit 100A main switch?

if so you can probably have your cake and eat it!!
 
Now might be a good time to sort out the poor access to the existing C.U

I was kind of thinking that.

if you put a big enough new consumer unit in, you could possibly re route most circuits to the new one with little effort.
it up to the customer if they want them all moving, you could possibly use the old CU as a junction box.
 
DB and one to 60A large switch that has a 45A fuse in
are you referring to a 60amp isolator possible a wylex.
[automerge]1580845991[/automerge]
so basically his question is can he have 2 DB
have you measured for a new board ,and is this work to be part p to local building control .
[automerge]1580846147[/automerge]
but i haven't been on the tools for a while and won't be doing the work but just trying to help a friend out.
so who is doing the work ?
 
Last edited:
Hi

Just a quick one, I am a qualified electrician but i haven't been on the tools for a while and won't be doing the work but just trying to help a friend out.
@buzzlightyear
he is not doing the work, he said it, so it must be assumed to be true!!
 
Haha can always rely on this forum for sarcastic answers

But this is similar to the wylex 60A installed...https://www.tlc-direct.co.uk/Products/WY108.html

Ive asked him to send me some photos of the situation
[automerge]1580847999[/automerge]
This are the photos he just sent me, there is about 50-60mm gap from boiler to DB
 

Attachments

  • 27513B53-2E4C-4D2C-9B31-77B78107FBC1.jpeg
    73.4 KB · Views: 46
  • 1E41C9D8-232C-42A0-979F-D2EBE3CC64DB.jpeg
    65.8 KB · Views: 46
Last edited:
The recent announcement about ripping out gas boilers and converting the whole country to electric may turn out to be fortuitously timed...
 
Given the cost of adding new ccts and a sub board it would not be prohibitively more expensive to change the entire board instead.
The gap looks a lot more than 50mm or so to me unless the photo is playing tricks on me! Wouldn't fancy changing it myself as does look tight to work in, but not impossible...
 
That’s one of those board changes you just look at and sigh.
the limited access would almost certainly put off 99% of busy sparks unless they were desperate for the work...
 
Thanks for all the replies, i know best case would be to do a DB swap but this is not feasible with the boiler in its current location. Can't even get a stubby in let alone a drill to mount a new DB/JB

So would a second DB not be another solution in this instance? It has 25mm Tails already and would only have a 3 circuits on it

He is panicking now about the cost of moving the boiler
 
Of course you can have a second DB, but I would be tempted to use the existing DB as a junction box and fit a new full size DB in a more convenient place as James suggested on page one.
 

Reply to Adding another DB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
473
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
881
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
702
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
616
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock